BFL13 wrote:
First suspect is the use of the extension cord(s). I found they increase the "load" as seen by the "source".
โNov-30-2018 10:44 AM
โNov-30-2018 10:18 AM
ktmrfs wrote:While I agree with this, and the cord is likely a non-issue, I was just trying to make the point that if the goal is to measure the generator, it's best to make at the measurements at the generator to get any other potential variables out of the picture.
a 40ft 12ga extension cord has a total resistance of 0.12 ohms.
now resistance is 9.8 ohms, or 12.25A or 1470 watts.
not much of an effect.
โNov-30-2018 08:37 AM
pnichols wrote:
The comments on loss of generator power at altitude got me thinking: Some (all?) built-in Onan RV generators have a convenient twist knob labeled as "altitude in feet" to adjust their air-fuel mixture if you need to use them at higher altitudes.
Is this type of easy adjustment right on the generator a rocket science feature? Why don't portable generators have a simple twist know to adjust air-fuel ratios versus altitude?
Messing with jet-changing seems an obsolete solution. I guess fuel injection gets around the need for this, so how does non-fuel-injection Onans do it?
โNov-30-2018 08:36 AM
โNov-30-2018 08:26 AM
2112 wrote:
More R = Less Load
An ideal 1500W heater would have a resistance of 9.6 ohms. At an ideal 120VAC it will draw 12.5A. Let's say an extension cord adds 1 ohm. Now R = 10.6 ohms.
120V/10.6 = 11.3A
120*11.3 = 1356W
The extension cord changed a 1500W load to a 1356W load.
โNov-30-2018 05:27 AM
2112 wrote:BFL13 wrote:What you are referring to is an inductive load such as your AC compressor and blower motor. They are trying to turn at a certain RPM. You can think of them as a constant power load due to when the voltage drops the current goes up to compensate for the lower voltage in order to maintain its speed. The motor requires a certain amount of power to maintain its torque. The high current demand of the AC causes a voltage drop across the extension cord. This is commonly referred to as IR. This voltage drop means there is less voltage at the AC. The longer the cord or the thinner the wires, the higher the IR.LittleBill wrote:
resistive loads work different, if the voltage drops, so does the load
Not sure it is the same thing now, but it is still true that when you are plugged into 15a shore power and run things in your RV, you will not pop the breaker so often if you are closer to the house and don't have such a long extension cord. Or if you change from a #14 to a #12 same length, you don't pop the breaker as much.
Isn't it the same thing when you are plugged into a generator's 15a receptacle?
A resistive load is a fixed load. When the voltage drops the current drops proportionally. One caveat to an electric heater is the coil resistance will change with temperature. It will draw slightly more current when you first turn it on. As it heats up the coil resistance goes up slightly, causing it to draw slightly less current.
โNov-30-2018 01:23 AM
BFL13 wrote:What you are referring to is an inductive load such as your AC compressor and blower motor. They are trying to turn at a certain RPM. You can think of them as a constant power load due to when the voltage drops the current goes up to compensate for the lower voltage in order to maintain its speed. The motor requires a certain amount of power to maintain its torque. The high current demand of the AC causes a voltage drop across the extension cord. This is commonly referred to as IR. This voltage drop means there is less voltage at the AC. The longer the cord or the thinner the wires, the higher the IR.LittleBill wrote:
resistive loads work different, if the voltage drops, so does the load
Not sure it is the same thing now, but it is still true that when you are plugged into 15a shore power and run things in your RV, you will not pop the breaker so often if you are closer to the house and don't have such a long extension cord. Or if you change from a #14 to a #12 same length, you don't pop the breaker as much.
Isn't it the same thing when you are plugged into a generator's 15a receptacle?
โNov-29-2018 08:04 AM
โNov-29-2018 07:37 AM
LittleBill wrote:
resistive loads work different, if the voltage drops, so does the load
โNov-29-2018 07:34 AM
LittleBill wrote:
resistive loads work different, if the voltage drops, so does the load
โNov-29-2018 05:59 AM
โNov-29-2018 04:41 AM
2112 wrote:
More R = Less Load
An ideal 1500W heater would have a resistance of 9.6 ohms. At an ideal 120VAC it will draw 12.5A. Let's say an extension cord adds 1 ohm. Now R = 10.6 ohms.
120V/10.6 = 11.3A
120*11.3 = 1356W
The extension cord changed a 1500W load to a 1356W load.
โNov-29-2018 02:09 AM
โNov-28-2018 06:22 PM
DrewE wrote:BFL13 wrote:LScamper wrote:
Long cord lowers load not increase it.
High altitude equal less air but same amount of fuel equal rich mixture.
Years ago I didn't understand when you told me current limiting was a way of keeping current constant. I thought you needed a way to keep the current up too. Later I got that.
So now I an stuck on how a longer cord (more R?) is less load.
Your heater or whatever on its own has a resistance R. Your longer cord adds a bit, for the resistance seen by the generator of R + a bit. Since the generator output voltage is supposed to be constant, by ohm's law the current (and hence power) is lower.
More generally, for a constant voltage source, the applied resistance is inversely related to the load. The minimum load is an open circuit, with no power being consumed; the maximum theoretical load is a short circuit with infinite power being consumed...but of course in real life you can't supply or dissipate infinite power, so something somewhere gives out, possibly with spectacular results.