I have this battery I got (on spec for me--took a chance) a year ago off a guy for $225 (Can).
https://cdn.enfsolar.com/Product/pdf/storage_system/5a695a7096504.pdf?_ga=2.18197561.14003359.155657...He had it in his basement for a couple years with several others he got for a project he never did. He said he charged them up every so often, and when I got it home it tested ok, so I thought I lucked out on my spec.
So after a year and using/abusing it in the usual way ( I am hard on batteries) but recharging it properly to 0.5/100 but not always at 20%, I tested it for capacity at the 20 hour rate.
It came up short, so I did an 8 hour condition run at 15.5v (16 as adjusted for temp) per Lifeline method, and re-tested.
Results follow, but hard to present the info--please struggle through to understand what happened. I will ask for interpretations, so yes- there is an exam!
๐I will show first a "normal" test using a three year old 100AH 27 AGM, then the Before with the big 8D, then the After with the 8D so you can compare normal loaded voltages over times at the 20 hr rate.
Time, Volts, Amps:
0600-start (resting full at 13.0v)
1100- 12.35, 5.1/ 11.9, 12.3/ 12.2, 12.2
1330- 12.1, 5.0 / 11.2, 12.0/ 10.3, 11.1
(lights dim and draw less as battery voltage falls, so the rate gets lower until you add a light)
So second test, way better voltage at first, but then loaded voltage crashed even worse than in the Before test after say 5 hours (out of 10)
In the Before, I stopped the test and voltage bounced right back to 12.4 (supposedly 50%) making capacity 85% of rated using AH drawn.
In the After, I stopped but the voltage bounced right back to 12.4 so I thought it would go higher after a little time, so I restarted the test. Now showing the 27, then the After.
1445- 12.0, 4.9, bounced back to 12.4, capacity 95.8% based on AH
After's results on re-starting: (added a light)
1345- 10.8, 12.5
1418- 10.2, 12.1
1430- 10.1, 12.0
1442- 10.0, 11.9 stopped , capacity comes to 90% based on AH and bounce back to 12.4 ---the bounce back was immediate from that loaded 10.0 to 12.3 (weird) and then it got to 12.4 in half an hour.
So just using AH down and 12.4 as 50% and allowing for temp reduction from 250 rated to 225 actual, 90% is not too bad.
BUT--that big crash in loaded voltage! Just weird. Can't be good.
Next weird thing, not seen before, is the recharge using 20% or over, with the 75 amp charger set to 14.8 (as adjusted for temp)
In the Before and After tests same thing-- instead of kicking off at 75 amps, amps started low and slowly climbed from 44 amps at first to 66 amps after five minutes and 70 amps after another five minutes.
I then jacked up the charger voltage to 15.1 and got the 75 amps. So reduced back to 14.8 and charging settled at about 68 amps then tapered as usual. (it should have hit 75 at first and stayed there for the Bulk stage) I had it down to 0.8a after the first test, so I expect the same today to indicate full (1.25a is 0.5/100).
OK--so what is going on here? I had no trouble with the battery bank (the 250 plus two 100s) last trip in March for a few days doing 50-9Os and ran the microwave etc, didn't see anything weird. Recharged ok at home. Nothing since that would damage anything.
The two 3 year old AGM 27s are doing ok, but this big 8D is having
"issues" being treated the same way looks like. At this time, it seems to be acting normally down to 75% SOC or so, then it goes crazy on the low loaded voltage. But it seems to still have decent AH capacity at 90% of rated. Banked with the two 27s nothing shows as weird down to 50% of 450. 50-90s seem to go well.
What's with that? Thanks