Bobbo wrote:Usnthedog wrote:
Checked continuity between ground and hot on the outside entrance plug.
Continuity between GROUND and HOT would be a dead short circuit and would trip the circuit breaker. What you need to check for is continuity between the NEUTRAL and GROUND. Make this check with the converter/charger breaker turned on since that is when you are seeing the problem. Continuity between NEUTRAL and GROUND would not trip a breaker, but it would trip a GFCI circuit.
โJul-19-2021 09:25 PM
โJul-19-2021 09:22 PM
โJul-19-2021 06:57 PM
Usnthedog wrote:
Checked continuity between ground and hot on the outside entrance plug.
โJul-19-2021 06:14 PM
โJul-19-2021 06:04 PM
โJul-19-2021 05:23 PM
Usnthedog wrote:
wa8yxm and 3 tons. Thanks. Please reread my OP. No hot water heater. (on demand propane only) Only with the converter breaker on doe it trip. Checked continuity between ground and hot on the outside entrance plug. No onboard generator. Refer on caused no problem. Only when the converter breaker is on. And please don't get upset with "please reread the post" it wasn't intended like you thought it was.
Thanks
Jeff