dougrainer wrote:
1. The First Bulletin said nothing about freeze ups. Just that they had a problem with leakers on 2 percent of the units. The problem cropped up in the first year of ownership, so if you had a suspect unit after 2 to 4 years, odds are yours is OK
No, it said that they had leakers. And the first symptom of a low charge is, wait for it, freeze ups. If you've got good airflow, high ambient temp and it freezes, the 99% probability is low on gas. Once that gas leaks out it stops cooling.
There's a rash of failed Dometics being reported all over the place from 2013 to today. Coincidence? Or Dometic trying to cover their butts to avoid a recall?
2. The 2nd link is 20(TWENTY) years old. The freeze sensor shown has been discontinued years ago(about 16 years). You will note that IT is installed at the bottom of the coil. YOU stated yours was in the MIDDLE, which is where the RV maker installed it, not Dometic. Sooo, if you had freeze ups on the 1st 2nd and maybe 3rd unit, LOOK AT YOUR INCOMPETANT Service person. They should have KNOWN the sensor was NOT in the correct place. At the bottom area of the coils about 1 to 2 inches up.
And in the failure mode of the 2nd unit it would have done NOTHING as the coil never froze at the BOTTOM where your document said it should go. Therefore since the unit was low on freon and freezing at the TOP of the coil the bottom was never cold enough to freeze. And yes it did freeze up. Ice shards in the ducts sound like glass breaking and I cleaned up numerous puddles that weekend.
Our service people are quire competent. Each time they resealed the divider better than the factory. Heck the last replacement they went to bat for us with Dometic to get that unit covered under warranty even though it was a few weeks out.
3. AS I STATED, if you had freeze ups, and had the Freeze Thermister and installed in the correct place, your units could not freeze up. Maybe not cool correctly but not freeze up.
Since I had a freeze up at the TOP of the coil and a correct sensor would be at the bottom of the coil, that's a LOT of freezing before it got to the sensor. In our case it never made it to the bottom.
4. I guess people do not need knowledgeable Service people, just look it up on the Internet. There is NEVER bad info on the Internet. Or info that when read, will be taken out of context.
5. Since you think searching the Internet makes you smarter than me, look at page 6 of this link. Doug
http://bryantrv.com/docs2/docs/ccc5.pdf
I have a good working knowledge of how an AC system works. How the parts work together. Have troubleshooted car and home ACs. I have close family members that are lifelong HVAC techs. Classic symptom of low gas is freeze ups if all the others are good. It's documented in many AC texts, on the Net, etc.
Having that sensor at the bottom would have done nothing in our case until the whole coil froze up.
I get that you are having a hard time being wrong but I know what ours experienced. Perhaps a refresher on AC theory and operation?
I know and have verified the symptoms with other HVAC techs. After replacing the units the AC works perfectly so something was wrong.