- Depending on how your OEM wired the system. The AC system is protected by a 3 amp fuse ON the upper AC control board. That means YOUR fuse is shorted by the 12 volt wire run from the Roof top to the wall tstat. That said, you need to state WHICH Dometic control system you have. There are up to 6 or 7 different ones. Also, your Furnace may be on that 15 amp fuse and there is a short between the Furnace and the upper AC control board. You need to state if you have Phone type wire connections or standard 7 wire multi strand AC/Furnace wiring. Year/Brand/Model of RV will also help. Doug
PS. you just joined. ALWAYS list Year/Brand/Model of RV and Brand and MODEL of the appliance when asking for help. - Tjpries1ExplorerThank you for your reply and information sorry for lack of details. It is 2008 Heartland Bighorn model 3400RL. The AC is Dometic model 59516.331. I see 6 wires on the t stat, not phone style. The control box is 3107541009. Also furnace does not work. The furnace has a 20 amp fuse in the fuse box, but it’s not blown. One odd thing I noticed is when I put a new fuse in(which blows immediately) the CCI LP gas alarm beeps and the lights on it go out. Any help is greatly appreciated, thank you
- Tjpries1ExplorerAlso I can hear and feel something clicking in the control box when I put a new fuse in
- Tjpries1ExplorerI think I need a new control box 3107541.009 but can’t seem to find one, looks like they are obsolete
- Label the wires at the control box. Disconnect the 2 BLUE wires at the AC control box and then see if the fuse blows. If it does , then disconnect the remaining wires and see if the fuse blows. DISCONNECT them at the control box. See if the fuse blows. Report back.
DO NOT REPLACE THE CONTROL BOX. This is a common error when novices work on a RV system. I have NEVER replaced a control box for a Dometic AC for a fuse blowing. This is with hundreds if not thousands of Dometic AC's over 42 years as an RV tech. Doug Tjpries1 wrote:
The clicking is the 12 volt relay on the control board. Normal. ODD that the LP detector is on the 20 amp circuit for the AC. Most OEM's install the LP detector on a 5 amp fuse at the main control panel. The short could be in the LP detector wiring. Doug- Tjpries1ExplorerI disconnected the blue wires for the furnace, still pops. I disconnected all the wires except the 12volt + and -, it still pops. Ac 6 pin is unhooked also. When I disconnect the 12v + from the control box the lp warning works fine and the fuse doesn’t pop
- Tjpries1ExplorerThere are 2 orange wire, 1 orange and 1 orange/white for 12+ Which are wire nutted to the red 12+ coming out of the box. There are 2 wires white and white/ orange wire nutted to the black 12- coming out of the box. With everything disconnected it doesn’t pop. But I did discover when I twist the 12- white and white/orange together (12v-) but with out the black wire to the box hooked up it pops, and the white/orange 12v- looks a bit discolored so it looks like the white/orange is the problem. Do you know why there would be 2 12v- wired together and where these wires come from/ go to?
The 6 pin is ALL 120 volt. The control box is just a galvanized box held in place with 1 or 2 screws. Drop the box and remove the 1/4 inch case cover screws. This will expose the Circuit board. Look for a shorted inside wire connection or melted connection. Turn the 120 breaker OFF for the AC unit when doing this. You have isolated the problem to the control box. The Dometic P/n you are looking at is for the complete Galvanized box and board, once you remove the cover you will see a Dometic P/n ON the control board. Usually starts with 31. Doug- Tjpries1ExplorerThanks, I have determined it is one of the 2 white/orange wires that are wire nutted together, going to the 12- , while I had everything disconnected and the box out I thought I would twist the two wires together and it popped, with the box sitting on the counter. Do you know where those 2 wires go/come from and are they 12 volt negative as the 12- indicates? Thank you
Having RV issues? Connect with others who have been in your shoes.24,188 PostsLatest Activity: Jan 19, 2025