โJan-01-2019 12:44 PM
โJan-02-2019 05:23 PM
โJan-02-2019 01:52 PM
โJan-02-2019 11:23 AM
Katdaddy wrote:jkwilson wrote:
The easiest check IMO is to get a power cord, crimp spade terminals on it to match the terminals on the electrical heating element, and plug that in in place of the refrigerator power cord. Let it run for a day. If it is cold, that proves the cooling unit works and your problem is on the control side.
But if that is the problem shouldn't it cool on gas?
โJan-02-2019 10:35 AM
Bud
USAF Retired
Pace Arrow
โJan-02-2019 10:27 AM
enblethen wrote:
I would suggest removing the circuit board and look at it closely for burnt areas. Arcing could have damaged more then just the 120 volt AC portion.
โJan-02-2019 10:17 AM
jkwilson wrote:
The easiest check IMO is to get a power cord, crimp spade terminals on it to match the terminals on the electrical heating element, and plug that in in place of the refrigerator power cord. Let it run for a day. If it is cold, that proves the cooling unit works and your problem is on the control side.
โJan-02-2019 09:00 AM
โJan-02-2019 07:44 AM
Bud
USAF Retired
Pace Arrow
โJan-02-2019 07:19 AM
โJan-01-2019 07:48 PM
โJan-01-2019 02:27 PM
โJan-01-2019 02:08 PM
enblethen wrote:
Sounds like either the 120 volt element is bad, no 120 volt AC tounit or the circuit board.
Verify 120 volts AC is present at refer by testing receptacle with known good device.
AC present switch refer to AC and test output of the circuit board for 120 volts.
No 120 volts circuit board is bad. Replace with Dinosaur electronics after-market.
AC present, disconnect the two wires from circuit board. Test element for resistance. Should be somewhere around 20-30 ohms.( I think)
โJan-01-2019 02:07 PM
โJan-01-2019 02:05 PM
Bud
USAF Retired
Pace Arrow