In the FURNACE mode the system will cycle the RV’s furnace On
and Off based on the room air temperature and the temperature
set-point on the Single Zone LCD thermostat. The system can be
configured to operate using an On/Off differential of either 1 degree
F or 2 degree F. This feature is programmed during the system initialization.
See “System Initialization” on page 3.
To set the temperature differential the system must be Off. Press
the “?” button and, while holding it, also press and hold the On/Off
Mode button for three seconds. Release the On/Off Mode button.
Then release the “?” button. Press the “+” button to toggle between
“d1” and “d2”, “d1” for 1 degree F differential and “d2” for 2 degrees
F differential.
System Initialization
A system initialization will need to be performed by the installer after
the system is installed.
• Make sure the Single Zone LCD thermostat is in the Off condition.
See page 4, “Quick Reference To Control Buttons”.
• Press the “+” button and, while holding it, also press and hold
the On/Off Mode button for three seconds. LCD will show
? ? . Press the On/Off Mode button again to turn system off.
This completes the initialization.
The furnace On/Off temperature differential should be set at this time.
See “Mode Description - Furnace” on page 9 for further information
on furnace mode differential setting.