SoundGuy wrote:
tmartin000 wrote:
Here is the question.....How fast is it? I really don't want my A/C causing the genet's output to stop overtime the compressor kicks in.
If I understand correctly you're asking what the EMS-HW30C's shut off response time is? :@ If so, I'd say based on my own unit that's it's "instant" ... yeah I know, not scientific but once voltage crosses either the low or high voltage threshold it shuts off "instantly". If the power source was my genset rather than shore power the moment the A/C compressor kicked on voltage drop would cause the relay inside the EMS to chatter ... solution is to remove the unit from the system when running on genset, ergo the reason I installed mine using 30 amp connectors. As far as surge protection is concerned the unit is spec to react in < 1 nanosecond.
As you're probably aware threshold voltages for the EMS-HW30C are 104 vac low and 132 vac high but that assumes the unit has been correctly calibrated. Mine wasn't but rather was reading almost 2 volts high and the result was it wouldn't shut off at 104 vac but closer to 102 vac ... fortunately the hard wire HW30C, unlike the sealed portable unit, can easily be re-calibrated provided you have a meter of known calibration.
yes, it is instant. it is driven by the pull in and drop out voltage of the relay. as mentioned you have some adjustment range, but at the low end, at some point the relay itself will drop out.
So....... Here is the BIG Problem you may encounter. generator bogs below 104V, relay trips out, generator recovers, relay kicks in, generator bogs, relay kicks out....... you get the picture. It will buzz like crazy and the generator will give fits, and the AC won't start.
That's what I've experienced even when using two honda 2000's in parallel IF they are in eco mode. Out of eco, fine. in eco, they can't recover fast enough to keep voltage above the dropout voltage.