RickLight wrote:
5. Electrical engineering is far more complex than presented. The short version is that such devices lower everyone else's voltage. Maybe one in 10 is OK, but 3 in 10? More? Overheating wires throughout the park IS a hazard.
The autoformer does increase the number of amps drawn, when park voltage is low. The breaker on a 30 amp or 50 amp service prevents it from damaging the campground wiring. The main breaker for the loop also protects the campground wiring. You can't draw more than the breakers allow, at least not for very long.
If NEC wants to truly protect wiring in RV parks--then they need to have many fewer pedestals for each loop. Iirc currently 13 30 amp pedestals are allowed per loop. Demand is calculated using 41% of full capacity. Have these numbers been changed?
Also plug in devices are NOT covered by NEC. One could argue that an RV is a "plug in device". Or you could simply use an autoformer as a plug in device.
As for myself, I limit my draw to 80% of the available outlets. i.e. 12 amps on a 15 amp, 24, on a 30, and 40 on a 50 (40 for each leg). I supplement that by using a hybrid inverter charger.