Glenn And Kitty wrote:
The gen is rated well above the capacity of the A/C and is evident that it is capable of easily handling the load(s) in eco mode as it only rises to 3050 RPMs from 2650 RPMs and does not go into overload. I don't usually do it so as to ease the load on the gen but, with the gen in eco mode, I have had on the A/C, microwave, coffee pot, and electric water heater all at once. The gen did kick up to full throttle speed (3450 RPMs), but it did not go into overload.
If the issue was happening in reverse, that the gen would go into overload when running on eco mode but would handle the A/C compressor kick on in full throttle mode, I would agree with the "hidden" usage idea but since it works fine at the lower eco mode RPM it must be something with the gen advancing when in full throttle mode, even though it should not, that is perhaps causing the overload.
โMar-13-2020 11:21 AM
โMar-12-2020 07:41 PM
ndrorder wrote:
When the generator is first started, the converter will be trying to charge the batteries. That can be a significant load in addition to the A/C. When turning things off, that should also include the breaker to the converter.
โMar-12-2020 01:18 PM
โMar-12-2020 01:10 PM
โMar-12-2020 01:06 PM
โMar-12-2020 01:02 PM
โMar-12-2020 12:51 PM
โMar-12-2020 12:24 PM
โMar-12-2020 11:22 AM
โMar-12-2020 09:49 AM
โMar-12-2020 09:26 AM
Glenn And Kitty wrote:You should start a gen in eco mode, otherwise it's full bore when cold. Your owner's manual should address this.
Gen start very easy and If it's OK to start the gen in eco mode I'll be good with that.
โMar-12-2020 08:11 AM