BB_TX wrote:
A GFCI trips when stray current leaks off to ground thru some unintended path. If you do not have a ground, it can’t leak off. And therefore the GFCI would never trip, even if it should. Lack of a good ground is not a good thing. And is also not safe for you. You need to correct that problem.
The path that the GFCI protects is between either the hot or (with a modern GFCI, neutral) to the earth through an individual. That "tickle" you feel with an ungrounded RV metal shell is what the GFCI is designed to prevent.
The US NEC allows (in fact, encourages) replacing 2 pole receptacles with GFCIs. They do not need a ground to function, although code does require labeling the 3 pole GFCI receptacles with a note that there is no ground connection.
There are lots of good reasons for carrying a non conducting ground throughout a facility or RV, but needing one for a GFCI to function is not one of them.