Hard Start kits: Supco SPP6 vs. Dometic #3310727.015

otrfun
Explorer II
Explorer II
Giving some serious thought to installing a hard-start kit on my 2012 Dometic 13,500 BTU Brisk Air a/c. Quite a few positive reviews on the Supco SPP6. Anybody have any experience using the Dometic Hard-Start Kit (#3310727.015)? Dometic claims their Hard-Start kit (or Starter Assist Kit) will dramatically reduce the LRA for their Brisk Air units. Thanks!
23 REPLIES 23

philh
Explorer II
Explorer II
Micro Air Easy Start is worth every penny. 2500 watt generator handles the air with no issue now.

otrfun
Explorer II
Explorer II
OP here. Learned a lot about inrush current/LRA in the last 6 years. Discovered start capacitors (with or without a PTCR) can potentially lower an RV a/c compressor's LRA about 3-5%. A Micro Air Easy Start (not available back in 2014) can lower a typical 55-70a RV a/c compressor's LRA as much as 50-60%---*huge* performance advantage vs. a standard start capacitor! Discovered paralleling two Honda EU2x00i's does double the continuous current output, but only increases the inrush current output about 10%. A whole lot cheaper (and a whole lot more effective) to purchase a $250-$300 Micro Air Easy Start vs. a $1000 2nd Honda to help reliably start an RV a/c.

joshuajim
Explorer II
Explorer II
Chris Bryant wrote:
There is virtually no difference between that Dometic part and the Supco SPP6- both are PTCR based start devices. Supco does not recommend the E series for RV applications- because if you shut the compressor and try to restart it right away, the E series will put the start cap in the circuit, a PTCR device will not. My response to that- doesn't short cycle the A/C (most new thermostats will not let you anyway).
DuoTherm does make a couple of better options- p/n 3102903.006 , which is a true potential relay (unlike the Supco "E" series quasi potential relay), and a really good, though very expensive start kit, the SmartStart- unlike anything else on the market (at ~$370, it better be ๐Ÿ™‚ ).

Another option I am looking at is the 5-2-1 compressor saver- a true 3 wire potential relay.

Note that the benefit for the non-PTCR type kits is really only in running off an undersized genset- they keep the start capacitor in the circuit until the compressor comes up to 75% of speed, which takes a fraction of a second longer if the genset bogs down.


I strongly agree with the 5-2-1 compressor saver. I was a Facilities Manager for a large school district fo 17 years.. We had thousands of 5 ton units here in the desert. The ONLY "hard start" kit that would consistently start old worn out units was the 5-2-1. We tried every brand available and the 5-2-1 was the best.
RVing since 1995.

jodeb720
Explorer
Explorer
The thing missing from this thread that didn't exist is the MicroStart technology - which didn't exist in 2014 and does now.

While I've not added one in lieu of my Supco unit - all the folks on this site speak favorably about it.

One thing to remember, as temperature climbs, so does the demand for electricity (in terms of Amp draw).

Generators lose 10% of their available output every 1000'.

Increase the temperature, and elevation and you're losing the ability to provide enough energy to drive the AC unit.

I'm not sure how the Microstart can (or does) mitigate that lower power output from the generator due to elevation and increase demand from the compressor due to temperature increase.

jjrbus
Explorer
Explorer
I got quite an education on this about 4 years ago. Most of the articles you find online the people have no idea what they are talking about or doing! Hint, as soon as they bring out a Kill a Watt meter, they don't have a clue. Takes a quality clamp on meter to measure inrush current.

My Honda 2000 would not start my Duo Therm 11k unit. Get a Suppco they said, will work 100%, easy to install. Put one in and wow! The AC fired right up, in 70 degree weather. Some place between 70 and upper 90's it failed to start the AC. Temperature, humidity and elevation affect AC and generator operation.

So on the net, at what point with a hard start running an AC that is oversized for the genset are brownout conditions experienced, at what temperature, at what elevation? How long will it take to burn out the AC or genny? The electronics in the Honda are in the $500 area, not something I want to make the wrong guess on.

If you try to run an air conditioner during a brown-out you risk damaging it permanently by burning the motor out. The reason is the air conditioners and many other motor driven appliances require a great deal more power to start than to continue running. If the power isnโ€™t available the motor continues to draw excess power none-the-less but fails to start and eventually overheats and burns out.

It is possible that modern appliances have protections to prevent this from happening but it has been a traditional problem so itโ€™s worth consulting the manufacturer to ask their advice.


So for me the options are bigger genny, smaller AC or a Micro Air soft start.

I was able to use an 8k window unit, which the Honda 2000 runs under all conditions. I did add a hard start to it, so I can run in ECO mode.

Only my opinion and worth what you are paying for it.

bikendan
Explorer
Explorer
Salinahocutt wrote:
Hard Start kit main function is that, increased compressor starting capacity and saver your compressor. It kick start to your compressor in your ***Link Removed***HVAC System. It is more faster, up to 10 times and more efficiently with your run capacitor. It so many issues like repair commercial refrigerator and freeze, multiple AC units problems, If your AC sometimes trips or shuts, etc. https://www.refrigerantrecoverymachine.com/best-hard-start-kit-hvac/


Holy Thread Resurrection, Batman!:S
A 6 year old thread brought to life!
Dan- Firefighter, Retired:C, Shawn- Musician/Entrepreneur:W, Zoe- Faithful Golden Retriever(RIP:(), 2014 Ford F150 3.5 EcoboostMax Tow pkg, 2016 PrimeTime TracerAIR 255 w/4pt Equalizer and 5 Mtn. bikes and 2 Road bikes

Salinahocutt
Explorer
Explorer
Hard Start kit main function is that, increased compressor starting capacity and saver your compressor. It kick start to your compressor in your ***Link Removed***HVAC System. It is more faster, up to 10 times and more efficiently with your run capacitor. It so many issues like repair commercial refrigerator and freeze, multiple AC units problems, If your AC sometimes trips or shuts, etc. https://www.refrigerantrecoverymachine.com/best-hard-start-kit-hvac/

Model# 8335D8564 ...?
Me-Her-the kids
2020 Ford F350 SD 6.7
2020 Redwood 3991RD Garnet

Chris_Bryant
Explorer II
Explorer II
ford truck guy wrote:
I read somewhere on this forum how you can tell if your AC already has a hard start kit on it by the serial numbers ?? I cannot find that thread , can anybody help? Chris Bryant >??


Only for Coleman (RVP) units- the second number of the second string tells what it has-
like 7333-6664
If that number is a 6, there is no start kit, a 7 means PTCR kit, 8 or 9 means a relay based kit.
-- Chris Bryant

I read somewhere on this forum how you can tell if your AC already has a hard start kit on it by the serial numbers ?? I cannot find that thread , can anybody help? Chris Bryant >??
Me-Her-the kids
2020 Ford F350 SD 6.7
2020 Redwood 3991RD Garnet

jodeb720
Explorer
Explorer
FWIW, On my 13.5 Coleman, I put the supp6e in mine and was able to start and run my AC on my 2000 - until it was really hot (outside temp) up to about 3000' (which is 500' less than Wayne's post earlier).

When it's really hot outside, the AC (if it's been off completely) will start, and run for between 10-20 mins before it exceeds the 13.3 that the Eu2000 will put out and overloads.

Without the supp6e, it would have started, at sea level, at 60 degrees outside.

my prior genny was a Yamaha 2400i and it ran a 13.5 coleman with a hard start kit no problem even when it was over 100 degrees outside.

If you want to run your AC in hot weather, it won't do it on just a single eu2000.

Chris_Bryant
Explorer II
Explorer II
They both would actually drop the current roughly the same- the difference between the PTCR and relay based units is that the relay based will keep the start capacitor in the line a bit longer if needed due to genset bogging down- the PTCR based ones can kick out before the compressor has actually started.
Only the SmartStart and maybe that SureStart (which looks interesting) will actually lower the current.

Here's a forum thread on Sailnet with a guy from Dometic who did some actual tests on current draw on startup.
-- Chris Bryant

otrfun
Explorer II
Explorer II
JeepCB wrote:
Food for thought, SPP6 cost me around $22 shipped. SPP6 is what SPPCO recommended for both my old 5er with avcoleman 13,500 and a buddies new trailer with 15,000 btu unit (don't remember the brand), they both worked great! Might want to go with the lower cost option first, just saying.
Good luck!
Billy
Appreciate the input, JeepCB.

DeepDiscountsco is selling the Supco SPP6 for $8.99 with free shipping on Amazon. Dyersonline.com is selling the Dometic #33102903.006 hard-start kit for $54.98 plus $8.49 shipping.

My 13,500 BTU a/c draws 12.2 amps (fan on high) with 60 amps of inrush startup current (actual clamp-on meter reading). I'm currently powering my Dometic 13,500 BTU a/c with two EU2000's. It's obvious they're being pushed hard (but, not struggling) everytime that compressor kicks on. My goal is to just reduce that 60 amps of inrush stress on my two EU2000's every time that compressor kicks on--not trying to run my a/c with one EU2000. Even if I could, 12.2 amps is way too close to one EU2000's maximum 13.3 amp current rating for my comfort level.

It sure would be nice to know how much the SPP6 and the Dometic kit each drop the inrush current(or LRA). Judging from Chris Bryant's post, I would assume the Dometic (#33102902.006) would drop more.

We'll see . . .

JeepCB
Explorer
Explorer
Food for thought, SPP6 cost me around $22 shipped. SPP6 is what SPPCO recommended for both my old 5er with avcoleman 13,500 and a buddies new trailer with 15,000 btu unit (don't remember the brand), they both worked great! Might want to go with the lower cost option first, just saying.
Good luck!
Billy
"Life is hard; it's harder when you're stupid" J.W.

2006 Dodge 3500 4x4 SRW QC/LB 5.9 CRD 6spd, w/Pacbrake.
2006 Denali 29rl-H5. 2 6V GC Batteries, but no solar yet.