dougrainer wrote:
If the outdoor Ambient condenser coil thermistor is defective or not connected all HP functions will shut down. This is ONLY RVP HP's and will not affect the COOL mode. So, if no fan or compressor, then I would check the condition of the condenser thermister. I have never seen one fail, so, I would suspect it is not connected to the upper control board. Doug
So could that condition("no connection to the upper control board")
be caused by a loose connection at the T stat ?
So far I have not gotten any tools out.Trying to get some education here before I really mess things up.
Thanks for the help from everyboby
Ed