3 tons wrote:Thanks for the clarification.otrfun wrote:I wasn’t confused, nor was I pointing out your ‘well put’ post, just trying to add a finer point of clarity for what’s often the uninitiated in the audience…
BTW, if you read any of my posts over the last few years (including the above three posts), I always make a point of referencing inrush current and LRA together (at least once) when discussing a/c compressors. I always do this to try and avoid any possible confusion. I assume you either missed it or you found it confusing?
3 tons
Apr-14-2023 05:12 PM
Apr-14-2023 03:21 PM
Apr-14-2023 03:18 PM
Apr-14-2023 03:14 PM
3 tons wrote:We also use a Honda 2200. Great unit, but yes, $$$.
I agree on the Micro-air, in my view a ‘must have’ and even with the micro-air, I upgraded from a Honda 2000 to a 2200 ($$), and due to elevation and/or higher ambient temps, and additional headroom - my point being, avoid scrimping on a generator because repurchasing is expensive!!
Also, in my case the pass-thru inverter would reject generator operation (and take over the load) as it saw ‘eco mode’ as a defective shore power condition…Adding another ATS as a work-around cured this nagging malady…BTW, to avoid any possible confusion, my air cond amperage spec’s refer to inrush as ‘LRA’ (Locked Rotor Amps) - just saying…
3 tons
Apr-14-2023 02:45 PM
Apr-14-2023 02:43 PM
otrfun wrote:
Is this *Supco* Soft Start you're referring to an aluminum-cased electrolyitc capacitor? If it is, they're only capable of reducing inrush current a few amps---very ineffective. A Micro Air Easy Start, a plastic box with circuitry inside, can reduce inrush current (LRA) as much as 25-40 amps. This is a massive, huge difference in capability.
Apr-14-2023 02:36 PM
Apr-14-2023 10:22 AM
jodeb720 wrote:They *both* lower inrush current (LRA). However, the Micro Air is 10-20 times more effective at lowering the LRA than a Supco Soft Start Cap electrolytic capacitor.
@Otrfun, correct it only helps with current inrush unlike the Microair . . .
Apr-14-2023 09:56 AM
3 tons wrote:All my continuous current recommendations assumed a Micro Air Easy Start was installed. LRA typically drops to 15-25a with one installed. With an LRA this low, starting in ECO mode is pretty much a given for the vast majority of 2000+ watt inverter generators. This assumes the generator is in good operating condition and it can support the a/c's continuous current reqt.
I would plan on sizing a generator that’s able to run the air conditioner while in the ‘eco’ mode.
3 tons
Apr-14-2023 08:01 AM
Apr-14-2023 07:49 AM
Apr-14-2023 07:13 AM
Apr-14-2023 07:04 AM
jodeb720 wrote:Is this *Supco* Soft Start you're referring to an aluminum-cased electrolyitc capacitor? If it is, they're only capable of reducing inrush current a few amps---very ineffective. A Micro Air Easy Start, a plastic box with circuitry inside, can reduce inrush current (LRA) as much as 25-40 amps. This is a massive, huge difference in capability.
I have a supco soft start on the AC unit already - which is how, I can get the 2000 to get the AC going; However, if i'm altitude or it's really hot, after 20 minutes it overloads the 2000's surge capacity.
Hence i'm looking at a bigger unit . . .