BFL13 wrote:
4/0 wire at 6 ft is crazy IMO. I saw that table from Xantrex. They appear to want too small a voltage drop.
If you're not FULLY loading the inverter, then the wire requirement is less.
But if you want to be able to supply a full 2KW from this inverter, then it NEEDS fat wire.
Here's a pic from the 2000 Watt load test I did with my Xantrex:
That's almost 208 Amps! A fully charged battery bank is 12.7V at rest. Under a heavy load, even fully charged, the voltage drops. A less than 1V drop causes the inverter to shutdown. Furthermore, as the voltage drops, the current requirement to do the same work goes UP. All wire has a voltage drop too. Thinner wire loses more voltage per foot.
This topic has come up a lot on the solar forums. It's also comes up in the inverter reviews on Amazon. People claiming their inverter won't supply the rated capacity. The two things that will cause this is undersized wire, and too small of a battery bank. That's not crazy, it's science. Same thing as hooking a garden hose to a fire hydrant. Fine for watering flowers, but if you need to use the higher flow for fighting a fire... you're hosed. :p
So what kind of expense is properly sized wire? I buy 4/0 welding cable (very flexible - 2054 strands) from Wesbell:
https://wesbellwireandcable.com/Welding/Welding4_0.htmlIt's $4.26/ft. 6' of black + 6' of red = 12ft x $4.26. $51.12 total. Go cheap, limit your inverter capacity. Spend $51, use it as advertised. Your choice.