wolfe10 wrote:It is correct and the open neutral is in the 120/240 CG distribution or split phase neutral if you like. I agree that if the hot or neutral is open to a 3 wire circuit there will be no voltage.CA Traveler wrote:Bobbo wrote:You can have very high voltage on 30A due to a open neutral. It happened to me and of course the open neutral was in the CG 120/240V distribution. This is I suspect a rare incident but it happened to me.
Correct me if I am wrong, but on a 30 amp circuit, you have a HOT and a NEUTRAL. If the NEUTRAL loses connection (which is what happened to fry his stuff) you have NO CONNECTION. You can only have the 0v and 240v (or low voltage/high voltage) difference if you have both HOTs connected with no NEUTRAL.
Fortunately I had installed a PI full power protector and it disconnected the rig power and no harm. The voltage was displayed on the remote and I could not pull the plug fast enough.
Sorry, not correct.
Yes, on 50 amp (two hots) and open neutral can cause very high/very low voltage.
But, an open neutral on a 30 amp (single hot) will just cause NO POWER.
โJul-29-2017 10:32 AM
โJul-29-2017 07:28 AM
โJul-28-2017 07:07 PM
wolfe10 wrote:CA Traveler wrote:Bobbo wrote:You can have very high voltage on 30A due to a open neutral. It happened to me and of course the open neutral was in the CG 120/240V distribution. This is I suspect a rare incident but it happened to me.
Correct me if I am wrong, but on a 30 amp circuit, you have a HOT and a NEUTRAL. If the NEUTRAL loses connection (which is what happened to fry his stuff) you have NO CONNECTION. You can only have the 0v and 240v (or low voltage/high voltage) difference if you have both HOTs connected with no NEUTRAL.
Fortunately I had installed a PI full power protector and it disconnected the rig power and no harm. The voltage was displayed on the remote and I could not pull the plug fast enough.
Sorry, not correct.
Yes, on 50 amp (two hots) and open neutral can cause very high/very low voltage.
But, an open neutral on a 30 amp (single hot) will just cause NO POWER.
โJul-28-2017 06:58 PM
mike-s wrote:Bobbo wrote:How many times has it refused to provide power because it sensed an issue?
FWIW, I bought my PI EMS-HW30C almost 10 years ago and have not plugged in a single time since without it
โJul-28-2017 04:26 PM
RSD559 wrote:
Which campground in Colorado Springs was this? It's good to know that they stepped up and took responsibility. We spent a week at the KOA there earlier this year. Speaking of that KOA, really great water park for the grandkids. It opened the day we left. I guess they open it up to outsiders for a fee. It was well populated. Our daughter said that she would bring the kids across town to play there when it's hot.
โJul-28-2017 02:03 PM
โJul-28-2017 01:57 PM
MEXICOWANDERER wrote:
That's called
TOUCH THE SKIN OF THE RIG AND NO NEED FOR MORNING COFFEE
โJul-28-2017 01:13 PM
CA Traveler wrote:Bobbo wrote:You can have very high voltage on 30A due to a open neutral. It happened to me and of course the open neutral was in the CG 120/240V distribution. This is I suspect a rare incident but it happened to me.
Correct me if I am wrong, but on a 30 amp circuit, you have a HOT and a NEUTRAL. If the NEUTRAL loses connection (which is what happened to fry his stuff) you have NO CONNECTION. You can only have the 0v and 240v (or low voltage/high voltage) difference if you have both HOTs connected with no NEUTRAL.
Fortunately I had installed a PI full power protector and it disconnected the rig power and no harm. The voltage was displayed on the remote and I could not pull the plug fast enough.
โJul-28-2017 12:55 PM
Bobbo wrote:You can have very high voltage on 30A due to a open neutral. It happened to me and of course the open neutral was in the CG 120/240V distribution. This is I suspect a rare incident but it happened to me.
Correct me if I am wrong, but on a 30 amp circuit, you have a HOT and a NEUTRAL. If the NEUTRAL loses connection (which is what happened to fry his stuff) you have NO CONNECTION. You can only have the 0v and 240v (or low voltage/high voltage) difference if you have both HOTs connected with no NEUTRAL.
โJul-28-2017 12:21 PM
Bobbo wrote:
FWIW, I bought my PI EMS-HW30C almost 10 years ago and have not plugged in a single time since without it
mike-s wrote:
How many times has it refused to provide power because it sensed an issue?
โJul-28-2017 11:17 AM
โJul-28-2017 08:04 AM
Bobbo wrote:How many times has it refused to provide power because it sensed an issue?
FWIW, I bought my PI EMS-HW30C almost 10 years ago and have not plugged in a single time since without it