Forum Discussion
BFL13
Mar 09, 2018Explorer II
How is the inverter 120v side wired up for what appliances are on what? IE is the MW on a different sub-panel from the other things that work ok? Try plugging in the MW to a receptacle that runs the kettle ok and see if the MW runs ok there.(will need an extension cord )
What is the 3a on standby compared with the 6a water heater? 3a 120v??? Makes no sense. Inverter on standby, no load, would have maybe 1/2 an amp DC although inverter/chargers seem to have more what with their extra "features".
What is the "output" all about? Not following. :(
Like the others, I have no problem running the MW with a 2000w inverter. But I don't have a remote display and transfer switch and relay etc. I plug the shore power cable into the Inverter and shut off the converter etc manually.
What is the 3a on standby compared with the 6a water heater? 3a 120v??? Makes no sense. Inverter on standby, no load, would have maybe 1/2 an amp DC although inverter/chargers seem to have more what with their extra "features".
What is the "output" all about? Not following. :(
Like the others, I have no problem running the MW with a 2000w inverter. But I don't have a remote display and transfer switch and relay etc. I plug the shore power cable into the Inverter and shut off the converter etc manually.