Harvard wrote:
Switching Mode Power Supplies and GFCIs
START QUOTE:
As explained earlier, RF noise filtration circuits in SMPS (Switching Mode Power Supply) generate intentional Earth Leakage Current. SMPS are used extensively as DC power sources in modern day electrical / electronic devices e.g. Audio / Video / Computing devices, power supplies, battery chargers etc. A single GFCI outlet / GFCI breaker may be serving multiple SMPS loads and therefore, will be sensing the sum of all the Earth Leakage Currents and, if the sum is > 4 to 6mA after connecting this unit, the GFCI will trip.
END QUOTE:
โJun-27-2019 06:31 PM
Kfry wrote:
Maybe u didn't under stand In my previous post I did narrow it down to the lights breaker when it's in the on position the gfci trips when that breaker is turned off and all other breakers are on the gfci doesnt trip . And the is a Gfci wall outlet on that circuit the lights are on . Thank you again