dougrainer wrote:
1. When a Roof AC has MANUAL controls, there is NO freeze sensor. It DOES have a Tstat, but it only senses the air return temp and NOT the evaporator
2. What you have experianced is NOT unusual. What you need to do is run on HI COOL and NOT Lo/Med-cool.
3. Some things may cause this that ARE fixable. You need to verify the stop gasket between the AIR RETURN and the COLD AIR discharge is tight and sealed and cannot bleed air thru which will also cause freeze up. AS others mentioned Dirty return filter, blocking off adequate warm air return.
4. Last as I mentioned before. This is normal depending on the outside temp and the humidity of the area you are in. Doug