nebmike wrote:This sounds like the burner is cycling probably due to inadequate airflow causing the high limit switch to open for the heat exchanger to cool. Listen very carefully and you should hear when the burner kicks back on. Harder to tell as it shuts down. Cycle maybe every 1 or 2 minutes.
Also, it seems as though every few minutes it'll blow cooler air for a while and then go back to somewhat warmer.
My main duct in the floor was collapsed as built new. Did my best to prop it open but the solution was to add two more ducts. I assume yours is different but similar issue.