BFL13 wrote:
Why keep the Victron 24-12 at 13.2 instead of say 12.6?
โJun-27-2017 05:21 AM
โJun-27-2017 04:15 AM
โJun-26-2017 05:30 PM
โMay-07-2017 04:01 PM
MEXICOWANDERER wrote:
THIRTY Volts WILL TIDE YOU OVER JUST FINE. This ain't a Betty Crocker moment.
CA Traveler wrote:
Using the most widely used temperature compensation formula:
-0.005 V per C per 2 V cell
Yields at 0C (32F) -0.005(0-25)12 = 1.5V for a 24V battery. And this implies that for ideal flooded bulk charging you would need a 29.6+1.5 or 31.1V charging source.
...
โMay-07-2017 09:20 AM
โMay-07-2017 08:19 AM
โMay-07-2017 06:59 AM
โMay-07-2017 05:56 AM
BFL13 wrote:
So when you go to the golf car place looking for their used battery deals you can pick 8v batts, not just their 12v batts.
The place I went to four years ago had 48v golf cars with 6-8s or 4-12s, and they seemed to be going over to the 8s for whatever reason.
I got two used 12v T-1275s, but you would be able to pick three-8s instead if you could fit them.
โMay-06-2017 07:16 PM
โMay-06-2017 05:15 AM
BFL13 wrote:
I got lost there but don't forget 30v at 24 is 15v at 12 and in winter, 14.8 at 12 is 15.2 at 12.
So in winter you need 30.4 at 24 just to stay even, OR, you can chicken out and go Down South for the winter. ๐
โMay-05-2017 10:33 PM
โMay-05-2017 06:52 PM
โMay-05-2017 01:11 PM
BFL13 wrote:
One thing not mentioned IIRC is that some (many?) solar controllers have a positive ground. That doesn't matter when you don't ground your panels as with an RV installation. I have no idea, but might that be a problem when using a pos grd solar controller supplied with a typical DC-DC? ISTR your 24-12 is chassis grounded? Not a clue, just mentioning it.
Rogue wrote:
The enclosure of the MPT-3048 is floating with respect to all circuit voltages and may be used with either negatively or positively grounded systems. It may also be used with systems in which neither negative nor positive are grounded, as allowed by NEC 690-41 for systems of less than 50 volts.