atreis wrote:
Wiring them in series lowers the line losses between the panels and the controller (it's amperage - the flow of electrons - that's resisted - and the higher voltage - how hard those electrons are being pushed - helps too). The MPPT controller will take care of outputting the correct voltage to the batteries.
When wiring different panels (or sets of panels) in parallel, the VoC should match as closely as possible. (If producing at all, most panels will produce they're rated voltage, even if they're mostly shaded and producing very low amperage.) If it doesn't, the lower of the two voltages is what will be used, with any difference wasted.
When wiring different panels (or sets of panels) in series, the VoC does't matter much (with an MPPT controller) but the Imp should match as closely as possible. If they don't match the higher-current panel will end up being limited to the same amperage as the lower-current panel with the difference wasted. (If the panels don't have bypass diodes, the same thing will happen if one of the panels is shaded. Some panels, Kyocera for instance, have bypass diodes between groups of cells as well. Some of the super-cheap panels don't have bypass diodes at all.)
There are many references online, some better than others, for the fun of wiring in series vs. parallel, and series-parallel. These are but a few:
Solar Facts
MPPT Solar
Solar Panels Venue
โOct-22-2014 05:38 PM
Cadillac Jack wrote:
I am after voltage. Higher voltage will push more amps into the batteries. Thus the MPPT controller.
Lower line loss, and more voltage.
Not sure why it matters that the batteries are in parallel.
โOct-22-2014 05:26 PM
โOct-22-2014 05:14 PM
โOct-22-2014 04:03 PM
โOct-22-2014 03:54 PM
NinerBikes wrote:
If you have two matching 120W panels, those are each close to 7 amps each charge rate. Why even bother screwing with the 50 watt solar panel and it's measly 2.5 addtional amps, when you already have 14 amps? Get another matching 120W panel if you can, and sell the 50 watt panel.
120W panels for 89 AH group 27's AGM's is plenty, for most applications.
Next time when your replace the Group 27's Trojans, consider 6V T105's instead. Much, much, much easier to keep charged, they don't have the crappy acid to lead ratios that car type sized batteries do, so that the damn battery can fit under the hood without shorting out at the terminals.
Trojan should make a T-105 AGM Side terminal batteries for cars already, for no shorts.
When you match batteries, you should match panels also... seems to me just to be common sense.
โOct-19-2014 10:56 AM
westend wrote:2oldman wrote:westend wrote:Not sure why that would be always true. It's pretty simple to try it and see the amperage reading at the controller.
Paralleling different panels with different electrical characteristics to one MPPT controller is not a good idea.
It is because the "knee" of the IV curve is different in the two different panels. That "knee" is where the MPPT controller observes the characteristics of the panel's output and determines how to sort voltage, amperage and resistance.
Think of it this way: The MPPT controller is lecherous. It likes to rub knees. If it has Charlise Theron in on one chair and Rosie O'donnell in another chair, it will get confused and start examining just Rosie's leg rather than Charlise's appendages. The result will not be pretty.
โOct-19-2014 10:15 AM
westend wrote:ARG!
.. it will get confused and start examining just Rosie's leg rather than Charlise's appendages. The result will not be pretty.
โOct-19-2014 10:05 AM
2oldman wrote:westend wrote:Not sure why that would be always true. It's pretty simple to try it and see the amperage reading at the controller.
Paralleling different panels with different electrical characteristics to one MPPT controller is not a good idea.
โOct-19-2014 09:55 AM
โOct-19-2014 09:52 AM
JiminDenver wrote:No, series would be worse. The amperage in the circuit would be that of the 50w panel.
Wouldn't the Rogue just handle all three panels in series? There would be nothing to confuse it then.