Your problem is the Motoraid feature causing the excess heat of the water in the Heater tank and causing the pressure rise from the heat of the water. Try this before your next trip. Doug
PS, The Atwood pop off valve psi trip is 125 to 150
PRESSURE-TEMPERATURE RELIEF VALVE
Weeping or dripping of a pressure-temperature relief valve while the water heater is running DOES NOT mean it is
defective. This is normal expansion of water as it is heated in the closed water system of a recreation vehicle. The
Atwood water heater tank is designed with an internal air gap at the top of the tank to reduce the possibility of weeping
and dripping. In time, the expanding water will absorb this air. To replace the air follow these steps:
Step 1: Turn off water heater
Step 2: Turn off incoming water supply
Step 3: Open the closest hot water faucet in the coach
Step 4: Pull handle of pressure-temperature relief valve straight out and allow water to flow until it stops.
Step 5: Allow pressure-temperature relief valve to snap shut, turn on water supply and close faucet