It seems the NEC in the US has an 80% rule, so you can only load a 15A to 12A etc. 3600 x 80% = 2880.The "80% rule" has context. It applies only to "continuous loads", where the maximum current is expected to continue for 3 hours or more. Absent that, circuits can be freely loaded to the maximum allowed by the wire size and OCPD.
โAug-08-2019 06:26 AM
โAug-08-2019 06:07 AM
wa8yxm wrote:The OP has already stated that his generator is an inverter type. Most inverter generators can be paralleled with the same model with an optional parallel cable.
Now .. I would not recommend you parallel it period
WHY. when you parallel two AC generators they must be precisely in phase. if they are out of phase bad things happen. These small ones do not phase lock well and may well go BOOM when you hook in the 2nd one.
โAug-08-2019 05:29 AM
BFL13 wrote:
"Running speed" is assumed to mean "continuous watts". So the 2300w gen does 1800w.
In ads for paralleling, they say it will double the output, but this is false. Two of those will not do 2 x 1800 = 3600. However, two of those might still be enough to run your air conditioner. Needs more info on the A/C's draw.
EG, a B&S "P2200" gen is rated at 1700w continuous. Paralleling those gets you maximum output of:
two P2200s = 3000 watts (not twice 1700 notice!)
one P2200 and one P3000= 3000w (which is more than the 3000's cont.)
two P3000s = 4800 watts
So you see how that works. It has much to do with the actual ratings of the receptacles on the "parallel kit". Each generator brand has its own versions of those and they vary.
In the table above, you see that the 2200 and 3000 combo is limited to 3000 same as for two 2200s. This is because you have to use the parallel kit that has the connections that fit the smaller gen parallel plug-ins. Same with odd size combos of other brands like Champion.
โAug-08-2019 05:18 AM
โAug-07-2019 06:14 PM
wa8yxm wrote:
YOu mentioned the Run Speed of 1800 (1/2 of 3600) This suggests to me it is a standard traditional Generator. NOT an inverter Generator for they do not have a "Run speed" they change speed as the load changes.
Now .. I would not recommend you parallel it period
WHY. when you parallel two AC generators they must be precisely in phase. if they are out of phase bad things happen. These small ones do not phase lock well and may well go BOOM when you hook in the 2nd one.
Now DC generators.. Well DC is always in phase.. (Unless you hook it up backwards)
Really big generators (Think Niagra Falls Power Plant) those can be effectively phase locked.
Inverter generators do it automatically for the most part
But I do not think that one can be phase locked for parallelling.
BUT.. There is hope
Vector Electronics makes a battery/inverter/charger system desgned to do what you need. The inverter syncs to your generator and when it senses a sudden load it kicks in.. then drops back to charge the battery.
I do not have a bookmark,, SOrry.
โAug-07-2019 06:09 PM
Groover wrote:
I would look into putting a Micro-Air easy start on the air conditioner. Expensive but still less than a second generator and a lot less trouble. It worked for me and there are a lot of YouTube videos on it. Easy start
โAug-07-2019 03:24 PM
โAug-07-2019 03:00 PM
โAug-07-2019 11:38 AM
โAug-07-2019 11:09 AM
scottsnider wrote:
I am sorry yes my Generator is a inverter type.
โAug-07-2019 10:14 AM
scottsnider wrote:
I am sorry yes my Generator is a inverter type.