If panel Isc is above 1.8 by a bunch, that display amps would be a problem. You could check panel direct and put your meter in line with one of the leads set to reading amps and check those amps vs Isc at the time. (As long as you don't expect 10 amps to blow the meter!)
If the lead-acid batt is a flooded type, it would be safe to let the voltage climb, but even an AGM starting at 12.4 should be ok long enough to take the amps readings.
If the lead-acid batt is a flooded type, it would be safe to let the voltage climb, but even an AGM starting at 12.4 should be ok long enough to take the amps readings.