Forum Discussion
outwestbound
Sep 06, 2017Explorer
pianotuna wrote:
Hi BFL13,
Equalization should only be done on AGM jars when loss of capacity is noticed. It needs to be done gingerly while monitoring temperatures and amperage draw. Charge voltage must be close to the gassing voltage (which is temperature dependent) but should NEVER exceed the gassing voltage. This has the quaint name of "dancing on the needles".
this equalization process is what concerns me about setting the BZ controllers to flooded, cuz it seems to say that it will equalize every 29 days @ 14.9Vdc. I'll call BZ and see if I can set equalization on manual for the flooded profile, if this makes sense.