Saw an ad for a "cheater plug" that supposedly uses an adapter that allows 50 amp service to be obtained by plugging one 30 and one 20 amp plug at the same time. Plug rig's 50 amp plug into one end, and other end has 1 30 amp and 1 20 amp plug to be put into pedestal at campsite. Anyone know if this can actually do as advertised? I'm skeptical.
Two young retirees restless to GO!
Life is too short to wait too long to do all we want to do!!
Go and enjoy!!
16 REPLIES 16

2_Retired
Explorer
Explorer
Thanks for the input. Thought it wasn't a good idea, and your posts confirm.
Two young retirees restless to GO!
Life is too short to wait too long to do all we want to do!!
Go and enjoy!!

myredracer
Explorer II
Explorer II
There is nothing wrong with having 2 GFCIs in series for safety or technical reasons. The only that will happen is when there is a ground fault, you can't predict which one will trip. Lots of info. on the internet about this. A good source is the mike holt electrical forum (for electricians, engineers, etc.). If the pedestal GFI trips, it could be due to leakage current in the shore power cord and/or the 20 amp GFCI is old and tired.

One downside could be increased voltage drop depending on how the pedestal is wired from it's supply source. If there's only one 30 and 20 amp on a pedestal in an older CG, it's likely fed by only a 120 volt 30 amp feeder as the NEC only allowed for a demand factor of 3600 watts for a 30/20 amp pedestal, thus a 30 amp feeder. Drawing 50 amps could cause a significant voltage drop. Nowadays pedestals are usually loop-fed with a heavy feeder (like 200 or 300 amps) and much less likely to be an issue. And as westernrvparkowner said, you could trip a 30 amp breaker back at the distribution panel that you have no access to.

The first thing I would do is measure the voltage at the pedestal. If it's rather low to start with, it's only going to get worse, and maybe a lot worse. Keep in mind too, that if running an AC unit in the summer and the voltage goes down, you'll draw even more current and that adapter may not help at all. Don't want to damage the AC either. Isn't one reason to have a 50 amp service to run a 2nd AC? How's that going to work with that adapter?

I wouldn't doing this sort of thing without an EMS. As mentioned, I think it's better to into load management mode. A generator would be a good thing to have for some situations if you have the space and $$ for one.

If you're heading to an older and unfamiliar CG, you just don't know what you'll find. The photo is from one of our trips last year. They had removed the 20 amp recept's. plus the pedestals were downright scary looking. They were all like that. We were at another older CG this year and the pedestal was 106 volts before even plugging in (plus had an open ground). The EMS kept tripping and we had to try 2 more sites to get usable voltage. No way this adapter would have worked at either CG.

A few years ago I read a post about a guy who called himself and electrician was going to make up his own home brew adapter to be able to plug into 3-4 adjacent pedestals to make up a 50 amp service. Despite everyone saying no, he was adamant it would work. Wish I could find the post...

Winged_One
Explorer
Explorer
I have had one for years. Got to use it once. Not very useful for the high cost. Almost all places we visit now (State Parks) have GFCI which kills it's usefulness. Shame, it worked slick before.

Unless you know for sure you will be able to use it, don't spend the money.

Good thing is many State Parks here are adding 50 amp, and we often get 50 amp service when we visit.
2013 F350 6.7 DRW SC Lariat
2011 Brookstone 354TS
Swivelwheel 58DW
1993 GL1500SE
Yamaha 3000ISEB

Old-Biscuit
Explorer III
Explorer III
Charlie D. wrote:

I may be missing something but I have never seen a breaker box with 2 30 amp receptacles. Wouldn't that be necessary foe that adapter to work?


Been is several CGs, usually ones that don;t have full hook ups but rather a 'Gang Box' with 4 30A receptacles.
Each rig backs in like the points on a map with power box in middle.

If 3 or less parked 1 RV could plug into 2 of the 30A receptacles.

Otherwise you could use a 30A to 15A adapter and use 30A & 15A receptacles provided the other issues didn't exist (GFCI/same circuit etc)
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

Charlie_D_
Explorer
Explorer
RoyB wrote:
This is a special adapter that connects two 30 amp outlets to a 50 amp outlet. By using adapters, 15 amp outlets can also be used. If two 30 amp outlets are used, you could get up to 60 total amps into you 50 amp service RV. This is not the normal 100 amps capability but better than only 30 amps.

Please NOTE the two two HOT pins will be feeding separate legs on the RV two separae 50AMP Electric ZONES in the trailer.



Like mentioned above you can use an adapter on one of the 30A MALE PLUS to adapt to the 20AMP Service plug.

You can find sources on-line for a molded version cheater cord like shown here...




As long as the rules are followed by keeping both HOT wires separated this idea is safe to use...

What you don't want to ever happen is having one MALE side plugged into a power source and it presents AC power to the unplugged MALE SIDE plug. This would be a dangerous situation. There should not be a way for this happen with a proper setup using the two 50-AMP SEPARATE ZONES in the RV 50AMP Distribution panel.

Usually speaking if you can order one from a well known suppplier like AMAZON it will be safe to use... Ordering one from home made EBAY source might be risky...

Roy Ken


I may be missing something but I have never seen a breaker box with 2 30 amp receptacles. Wouldn't that be necessary foe that adapter to work?
Enjoying Your Freedom?
Thank A Veteran
Native Texan
2013 Prime Time Crusader 330MKS
2018 Chevy 2500 D/A Z71 4x4 Offroad
2006 Holiday Rambler Savoy 33SKT-40,000 trouble free miles-retired
2006 Chevy 2500 D/A-retired
2013 Chevy 2500 D/A-retired

DrewE
Explorer II
Explorer II
I don't like these cheaters, and frankly I'm a bit surprised they're sold on the open market. They have a number of problems, mostly related to the necessity of tying the neutrals together.

First, they quite properly trip any ground fault circuit interrupter they're plugged into. This precludes their use in a great many places to start with, as the 20A outlet is required by the current electric code to be GFCI protected.

Second, if there's a miswired outlet with incorrect polarity (neutral and hot swapped), they produce a short circuit. Hopefully there's a good circuit breaker in the systemโ€”and it's on the actual hot lead, not the putative hot lead.

Third, if there's an open neutral in one of the outlets and they're both wired to the same leg, the system works properly, but the remaining neutral is overloaded, potentially quite substantially.

Finally, if you happen to have any 240V loads in your coach and one of the sides is unplugged, the male plug will be hot. 240V loads are not at all common in RVs, so this isn't very likely in practice; indeed, most 50A RV electric panels aren't configured to even be able to have a 240V load.

Dennis_M_M
Explorer
Explorer
We have one, only used it in an older campground in Florida a number of years ago. Did the trick for us then, have not had a need for it since.
'99 Volvo VNL610 - 425 HP Volvo; Super 10 Spd
'13 smart CityFlame on Volvo
'05 Newmar Mountain Aire 35 BLKS
Trailer Saver; Bigfoot; Pressure-Pro.
Our Travel Blog - A New Adventure

RoyB
Explorer II
Explorer II
This is a special adapter that connects two 30 amp outlets to a 50 amp outlet. By using adapters, 15 amp outlets can also be used. If two 30 amp outlets are used, you could get up to 60 total amps into you 50 amp service RV. This is not the normal 100 amps capability but better than only 30 amps.

Please NOTE the two two HOT pins will be feeding separate legs on the RV two separae 50AMP Electric ZONES in the trailer.



Like mentioned above you can use an adapter on one of the 30A MALE PLUS to adapt to the 20AMP Service plug.

You can find sources on-line for a molded version cheater cord like shown here...



As long as the rules are followed by keeping both HOT wires separated this idea is safe to use...

What you don't want to ever happen is having one MALE side plugged into a power source and it presents AC power to the unplugged MALE SIDE plug. This would be a dangerous situation. There should not be a way for this happen with a proper setup using the two 50-AMP SEPARATE ZONES in the RV 50AMP Distribution panel.

Usually speaking if you can order one from a well known suppplier like AMAZON it will be safe to use... Ordering one from home made EBAY source might be risky...

Roy Ken
My Posts are IMHO based on my experiences - Words in CAPS does not mean I am shouting
Roy - Carolyn
RETIRED DOAF/DON/DOD/CONTR RADIO TECH (42yrs)
K9PHT (Since 1957) 146.52M
2010 F150, 5.4,3:73 Gears,SCab
2008 Starcraft 14RT EU2000i GEN
2005 Flagstaff 8528RESS

time2roll
Nomad
Nomad
Just get a 30/50 adapter and watch your power usage.
Everything still works... just not all at once.

westernrvparkow
Explorer
Explorer
Two other problems. One, the pedestal is likely not wired with both legs of the electrical service. This means that any energy management system in your rv will only see 120 volts when it measures the voltage across the two lines that feed the distribution system. The management system's programming then act as if the system is connected to a 30 amp service and will run all your electrical systems accordingly. Then there is also a very good possibility that the 30 amp breaker and the 20 amp breaker are either tied together or the pedestal is wired back to the distribution panel and is protected by a 30 amp breaker there as well as at the pedestal. So even if neither breaker in the box is tripped, you may very well trip a breaker at the distribution panel, and you probably don't have access to that breaker to turn it back on.
Those cheaters are generally not very useful.

wa8yxm
Explorer III
Explorer III
newman fulltimer wrote:
Been around for years yes they work


Correction: Yes they work.. IN very few places.

The problem is the electrical code, In most parks today the 20 amp outlet is GFCI protected and in some cases so is the 30 amp.

These devices will not work if one, or both, outlets are GFCI.

I have one, I have used it (Successfuly) in only 2 places.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

mkirsch
Nomad II
Nomad II
You won't be able to run everything, but you will have power to everything in the RV at least.

Putting 10-ply tires on half ton trucks since aught-four.

SoundGuy
Explorer
Explorer
2 Retired wrote:
Saw an ad for a "cheater plug" that supposedly uses an adapter that allows 50 amp service to be obtained by plugging one 30 and one 20 amp plug at the same time. Plug rig's 50 amp plug into one end, and other end has 1 30 amp and 1 20 amp plug to be put into pedestal at campsite. Anyone know if this can actually do as advertised? I'm skeptical.


Presumably you understand that so-called "50 amp service" is really 100 amp service because it's 50 amps per leg across two legs for a total service of 12,000 watts whereas 30 amp service is 30 amps across one leg for a total service of just 3600 watts. Use this cheater and you'd have up to 6000 watts available, half that offered by "50 amp service".
2012 Silverado 1500 Crew Cab
2014 Coachmen Freedom Express 192RBS
2003 Fleetwood Yuma * 2008 K-Z Spree 240BH-LX
2007 TrailCruiser C21RBH * 2000 Fleetwood Santa Fe
1998 Jayco 10UD * 1969 Coleman CT380

Old-Biscuit
Explorer III
Explorer III
Yes they will give you 50A total.........

One hot leg will have 30A ability and other leg will have 20A ability

Won't work if 20A is a GFCI or if 30A and 20A are on same circuit
Is it time for your medication or mine?