โMar-16-2017 05:54 PM
โApr-02-2017 06:21 PM
DieselBurps wrote:
UPDATE:
Well I installed the easy start soft start thingy, in the parking lot of a Napa auto parts store in 93 deg. heat no less. I was able to find another store that would let me barrow their 120 volt utility power to do the 5 starts of air conditioner like Easy Start recommends. Success, it works.
I then went back to my place to try it on the single Honda 2000 watt genny, it started the AC no problem, no brownout or anything. Started the AC in eco mode and ran it at about half throttle or so my guess in eco mode. Really pretty quite.
โApr-02-2017 05:51 PM
โMar-23-2017 04:41 PM
SoundGuy wrote:pnichols wrote:
What leaving this main circulation fan ON all of the time means with respect to generator loading is ... the air conditioner's start up current loading (compressor locked rotor large current spike plus main circulation fan locked shaft smaller current spike) on the generator is reduced because the main circulation fan is already running whenever the compressor starts.
OTOH one can eliminate fan load entirely upon initial start up by installing an SPDT switch with a centre off position to the A/C thermostat ... allow the compressor to come up to speed, then turn on the fan ... one of the tricks I used to enable my EU2000i to start our 13,500 BTU Mach 3+ A/C. I wish the Micro-Air Easy Start had been available then and I was aware of it as I'm confident that would have been the better solution. ๐
โMar-23-2017 11:42 AM
pnichols wrote:
What leaving this main circulation fan ON all of the time means with respect to generator loading is ... the air conditioner's start up current loading (compressor locked rotor large current spike plus main circulation fan locked shaft smaller current spike) on the generator is reduced because the main circulation fan is already running whenever the compressor starts.
โMar-23-2017 10:28 AM
โMar-23-2017 10:02 AM
โMar-23-2017 09:23 AM
DieselBurps wrote:Glad to be here to help!
With my A/C turned on and when the compressor cycles or kicks off, the fan continues to run, so the fan timed delay seems like it would only matter on initial start up? Maybe the easy start compressor start sequence is enough to enable my A/C to cycle back on with the Honda generator in ECO mode?
โMar-23-2017 08:29 AM
Dieselburps - Your situation is a bit atypical since most of the time, a 2000W generator will not start a rooftop A/C of 13.5kBTUs or larger without an EasyStart. What BTU size does your truck camper have?
EasyStart also allows you to run the generator with ECO mode turned on, so you can maximize fuel economy
Then, when the A/C's thermostat calls for cooling again, the fan will start up first, but the EasyStart then intentionally delays the compressor startup for a minimum of 5 seconds. The fan's current load is enough to cause the generator to exit ECO mode and jump to high-RPM (full power), so by the time the EasyStart begins its compressor startup sequence, the generator has attained full RPM and full power.
โMar-23-2017 12:52 AM
RSD559 wrote:RSD599 - The reason the EasyStart can reduce the amps so dramatically is because it is truly a sophisticated, microprocessor-controlled device, that uses advanced power electronics to carefully orchestrate the compressor startup using a gentle voltage ramp, with realtime closed-loop rotational and current feedback. Both the hardware and the firmware are quite advanced, and it's taken us over 4 years to perfect it. EasyStart has and continues to be built-in by many OEMs into various types of A/C products, mostly marine and trucking applications. Our deeper involvement with RV rooftop applications started last summer, pretty much by accident, since we had no idea the market was such a good fit. THe need for EasyStart is driven by the need to start and run a typical RV rooftop A/C on the gold standard, 2000W generators. More on that below.
Item #2, how can it reduce start-up amps so drastically? It would be interesting to see if anyone has actually checked that claim out.
DieselBurps wrote:Dieselburps - Your situation is a bit atypical since most of the time, a 2000W generator will not start a rooftop A/C of 13.5kBTUs or larger without an EasyStart. What BTU size does your truck camper have? I know of one brand of truck camper that uses the 9.2kBTU Coleman rooftops, and those do typically start on 2000W generators with the factory-installed hardstart kits. But besides the obvious benefit of allowing your (13.5 or 15k) A/C to reliably start and run on a 2000W generator, EasyStart also allows you to run the generator with ECO mode turned on, so you can maximize fuel economy. I know you are most interested in this, so here's how it accomplishes that. During the night when the A/C might cycle off, with ECO mode turned on and as you are already aware, the generator will drop to its low RPM. Then, when the A/C's thermostat calls for cooling again, the fan will start up first, but the EasyStart then intentionally delays the compressor startup for a minimum of 5 seconds. The fan's current load is enough to cause the generator to exit ECO mode and jump to high-RPM (full power), so by the time the EasyStart begins its compressor startup sequence, the generator has attained full RPM and full power.
Thanks for breaking it all down for me.
I should provide an update. Well, I still have the yamaha 2000IS watt inverter generator but I picked up a brand new HONDA EU2000 for $750. I plan to sell the Yamaha.
Here is the test I conducted today, approximate stats, new generator, near sea level, not that hot out.
The Honda starts my truck campers AC unit with ECO mode OFF, no problem, no overload lights. It will also keep the AC running with ECO mode ON, it dials down the RPM's a bit, it is quite, at least enough for me. I am happy.
Challenges will be different environmental conditions, and the AC cycling on and off. I think this is where option #2 with a micro air or similar hard start kit comes in.
I need to research that now, and figure out how it works with an AC cycling on and off.
โMar-22-2017 06:46 PM
If you have an RV a/c unit which your solo EU2000i is unable to reliably start (under all conditions) because of a LRA greater than ~50 amps then you have have 4 options (least to most expensive):
1) Purchase/install a generic, inexpensive hard start kit for $10-$30. An effective option . . . if your a/c unit does not have one already installed. Many units have OEM hard start kits already installed at the factory. These kits can potentially reduce the LRA approx. ~10 percent---enough to improve starting characteristics in some situations. If your a/c unit already has one installed and/or your unit still won't start reliably after installing one, then on to option #2.
2) Purchase/install the more advanced, micro-processor controlled, Micro Air Easy Start kit for $300 - $350. This kit comes highly touted by some here. If the MAES kit does reduce the LRA 65-75 percent as advertised, then it is, indeed, a miracle device
3) Replace your current RV a/c unit with a unit that has a lower LRA (<=50a) for approx. $550 (on sale) - $800.
4) Purchase another EU2000i to parallel with your existing EU2000i for $900-$1000. Note: paralleling two EU2000i only increases the total inrush current capability (necessary to satisfy the a/c unit's LRA) approx. 10 percent (vs. one EU2000i). On a/c units with LRA's as high as 60 - 65 amps, you may need to run both EU2000i's with the Eco mode off to reliably start. On RV a/c units with extremely high LRA's (65 - 70 amps) a paralleled pair of EU2000i's may have trouble reliably starting these units even with the Eco mode off.
For those who have not yet purchased a second EU2000i or a RV a/c unit, highly suggest the purchase of an RV a/c unit with a LRA of 50 amps or lower in order to forego the expense of hard/soft start kits and/or a second EU2000i generator.
โMar-22-2017 05:34 PM
RSD559 wrote:
Item #2, how can it reduce start-up amps so drastically? It would be interesting to see if anyone has actually checked that claim out.
โMar-22-2017 04:51 PM
otrfun wrote:RSD559 wrote:If you have an RV a/c unit which your solo EU2000i is unable to reliably start (under all conditions) because of a LRA greater than ~50 amps then you have have 4 options (least to most expensive):
Not trying to argue here, but what is the difference between an Easy Start kit and a hard start kit? Is there something more to the Easy Start? I've seen posts where people are running their 13,600 A/C with a 2000 watt generator. My Honda EU3000is wouldn't start my 13,600 without the hard start capacitors on the A/C. So they must be doing something!
1) Purchase/install a generic, inexpensive hard start kit for $10-$30. An effective option . . . if your a/c unit does not have one already installed. Many units have OEM hard start kits already installed at the factory. These kits can potentially reduce the LRA approx. ~10 percent---enough to improve starting characteristics in some situations. If your a/c unit already has one installed and/or your unit still won't start reliably after installing one, then on to option #2.
2) Purchase/install the more advanced, micro-processor controlled, Micro Air Easy Start kit for $300 - $350. This kit comes highly touted by some here. If the MAES kit does reduce the LRA 65-75 percent as advertised, then it is, indeed, a miracle device ๐
3) Replace your current RV a/c unit with a unit that has a lower LRA (<=50a) for approx. $550 (on sale) - $800.
4) Purchase another EU2000i to parallel with your existing EU2000i for $900-$1000. Note: paralleling two EU2000i only increases the total inrush current capability (necessary to satisfy the a/c unit's LRA) approx. 10 percent (vs. one EU2000i). On a/c units with LRA's as high as 60 - 65 amps, you may need to run both EU2000i's with the Eco mode off to reliably start. On RV a/c units with extremely high LRA's (65 - 70 amps) a paralleled pair of EU2000i's may have trouble reliably starting these units even with the Eco mode off.
For those who have not yet purchased a second EU2000i or a RV a/c unit, highly suggest the purchase of an RV a/c unit with a LRA of 50 amps or lower in order to forego the expense of hard/soft start kits and/or a second EU2000i generator.
โMar-22-2017 11:19 AM
RSD559 wrote:If you have an RV a/c unit which your solo EU2000i is unable to reliably start (under all conditions) because of a LRA greater than ~50 amps then you have have 4 options (least to most expensive):
Not trying to argue here, but what is the difference between an Easy Start kit and a hard start kit? Is there something more to the Easy Start? I've seen posts where people are running their 13,600 A/C with a 2000 watt generator. My Honda EU3000is wouldn't start my 13,600 without the hard start capacitors on the A/C. So they must be doing something!
โMar-21-2017 11:52 AM
SoundGuy wrote:rockwind1 wrote:
i run my 13,500 btu dometic on two hondas in parallel, no eco for starting. but i am interested in that soft start kit but **** it's expensive. anyone had any experience with them. is it made in usa?RSD559 wrote:
The one in the ads is. You can get a generic kit for $30 or $40 online. Here's an example. This one is for Dometic units.
Dometic Hard Start Kit
You basically have to pull the cover off the AC unit and follow the directions on where to plug the leads in.e
Two entirely different animals. Expensive? ... sell one of the Hondas, use part of the proceeds to pay for an Easy Start which is not the same as that Dometic hard start kit, pocket the difference, and enjoy the simplicity of powering your A/C with just one 2K genset. I don't see where the debate is but if you want testimonials just search this site for Easy Start. In the meantime here's an interesting Micro-Air Easy Start YouTube Video on how to install one of these units. ๐