The Official unofficial CPE 2000i Generator Thread

pritch272
Explorer
Explorer
8/1/2010 edit: Thread renamed at the suggestion of the Professor.
Renamed from: Champion Inverter and Remote Gens Promo on CPE's web site)


3/22/2011 edit: Thread renamed ...
Renamed from: Official CPE 2000 Watt Inverter Generator Thread


3/23/2011 edit: Thread renamed at the suggestion of the Professor.
Renamed from: (Un)Official CPE 2000 Watt Inverter Generator Thread


Inverter Available August 2010



Remote Available July 2010

2007 Keystone Laredo 29RL, 2000 Ford F250 7.3 PSD, Firestone bags, Pressure Pro, 16" Michelin XPS Ribs, MorRyde Pin Box, Dexter EZ-Flex, PI EMS-HW30C, Dirt Devil CV950 Central Vacuum, 2000W AllPower by Kipor, 4000/3500W Champion C46540
2,927 REPLIES 2,927

nitrohorse
Explorer
Explorer
Beachums wrote:
By no means was I attacking them about what the guy was asking. When I re-read my post I felt it looked as though I was knocking them. I was just referring to the logistics behind actually diagnosing the problem. I would expect any company who is resposible to ask of me what he is . I actually look forward to it. If nothing else, it will point me in the right direction with getting the A.C. to work.


I too worked with the Champion techs to resolve a small burbing issue when on eco mode. I think you will be pleasantly surprised at how sincere and genuine the techs
are when working with a customer. They never asked me to provide a receipt or a warranty card registration number, it was just their will to help that impressed me.

MrRchitty
Explorer
Explorer
I tested my capacitors and they measured just a pinch above what they were rated for.

I still have the issue of not being able to start my Dometic 13.5k AC unit with the twin Champs.

Down at the fire station, looking at our Safety Smoke Trailer. It has an AC unit, I can't find anywhere what size it is. However, mine at home is rated at 58 amp start and 11.6 amps running. When I test it, that is about what I get.

The Safety Trailer, I had the cover off about a month ago because it was tripping a 20 amp breaker on the Honda 5000 open frame genny. Testing the capacitors and the load, (I forget the start up) but the load running was 15 amps (rating on sticker) which is what I get on the clamp meter. This is with the fan on high. So, is this unit a 15k AC unit? It is by Coleman. (Can't find any info on it)

Bring the twin Champs in to see what it does with the Coleman. With eco mode on, they go into overload. With eco mode off it starts the ac unit without any problems. I remember when I had the cover off of this unit, the capacitor looked different and appeared to have some other electronic component to it. The Safety Trailer is made to run on generator. After all it is a free standing unit that is towed to schools and other areas to teach children about fire safety. You don't have a 30 amp outlet everywhere we go. So, I am assuming this AC unit is built with a start unit capable to be handled by generators without issue.

My Springdale, however, is made to be taken campground to campground, my opinion, of course, and perhaps a cost factor as well. So, perhaps, one RV AC unit manufacturer does something a little different than another for situations such as these....

I am still in search of the SPP6E to see if this will help. There is supposed to be added benefits with the E in the part number.

And so it goes.....
Randall J. Chittenden
CT
Fire/Medic
Former Auto Parts Sales 12 years

Beachums
Explorer
Explorer
By no means was I attacking them about what the guy was asking. When I re-read my post I felt it looked as though I was knocking them. I was just referring to the logistics behind actually diagnosing the problem. I would expect any company who is resposible to ask of me what he is . I actually look forward to it. If nothing else, it will point me in the right direction with getting the A.C. to work.
2004 Ford Expedition 4X4 3.73 w/quick shift kit
Reese DC Straight Line/ Prodigy P2 Controller
2010 Coleman CT 250 GS

PrivatePilot
Explorer
Explorer
As long as you do what they ask for diagnostics, I think that you'll find Champion is exceptionally good with their customer service. I know that they've bent over backwards to help a lot of people that had the burping issues, etc.

They were actually here in this thread for quite a while trying to help people directly before they were told they weren't welcome because they're not a vendor, but pretty much everybody (including myself) that have ever contacted them directly have always had good experiences.
30' Keystone Cougar 5'er, Triple Bunkhouse, SuperSlide.
Chevy 3500 1 Ton long box crew cab dually
6.5 Turbo Diesel, 4.11 Rears, LSD, Fresh rebuild spring 2012.
Dieselplace.com Staff Member

Our 2008 western adventure - to the coast and back!

Mark

Beachums
Explorer
Explorer
I just called CPE. I explained the situation and he told me he could not do anymore troubleshooting without the genset and load device in front of me. So now I have to get my trailer back from storage and get my gens out only to try and catch these guys during business hours.......this will be fun.
2004 Ford Expedition 4X4 3.73 w/quick shift kit
Reese DC Straight Line/ Prodigy P2 Controller
2010 Coleman CT 250 GS

MrRchitty
Explorer
Explorer
PrivatePilot wrote:
Although the converter and the 120V circuitry, breakers, etc. commonly share a single spot in the trailer, they are two distinctly different units under the hood.

Typically the only interconnection between the two is where the converter power source wires run to the 120 V side and draw power for the converter.

On my trailer the converter is wired to the same circuit breaker as almost every since receptacle in the trailer, with the exception of the one that the microwave is plugged into in the cabinet, and the one outside GFI plug...so when that breaker is off, so is the converted.

As part of my modifications try to get my air conditioner to run on a smaller generator that I owned at one point, I actually installed a toggle switch next to the converter that allows me to shut it off without having to cut power to all the other receptacles in the trailer. Although I don't think that's necessary in your case, it is an option if you find out that the converter is somehow hardwired in such a way that turning breakers off won't kill the power to it.


My converter shared a circuit breaker with many outlets, too. My panel had room for additional breakers, thus I added 2 more. I cut the wire which was tied to the converter and plugs and gave the converter its own breaker.

I too have problems starting my AC unit. I put a toggle to the blower relay inside the air handler to cut the blower on the low side. With the gensets running with eco off, I can start the compressor. Then I flip the blower on. I tried a hard start capacitor #spp7. That was before I bought the Champion models. The capacitor ultimately failed. I now have a clamp meter capable of testing and reading the capacity of the original capacitors. If time permits today, I'll see if they are good. I checked local supply and nobody had the spp6e. Our safety Trailer at the Firehouse was able to be started with another Chinese knockoff inverter generator. On checking the AC unit, the capacitors looked a little different. This trailer was set up for generator use initially.

My modules have both been changed out. The spec on the shipping paper indicated non-exterior breaker. Since changing the modules, I have been able to reliably start my pancake compressor, electric power washer and skill saw with no issues. It is just the AC unit. Anyhow, time to put my daughter to bed and get the kids outside and take the AC unit apart and check those capacitors.
Randall J. Chittenden
CT
Fire/Medic
Former Auto Parts Sales 12 years

PrivatePilot
Explorer
Explorer
Although the converter and the 120V circuitry, breakers, etc. commonly share a single spot in the trailer, they are two distinctly different units under the hood.

Typically the only interconnection between the two is where the converter power source wires run to the 120 V side and draw power for the converter.

On my trailer the converter is wired to the same circuit breaker as almost every since receptacle in the trailer, with the exception of the one that the microwave is plugged into in the cabinet, and the one outside GFI plug...so when that breaker is off, so is the converted.

As part of my modifications try to get my air conditioner to run on a smaller generator that I owned at one point, I actually installed a toggle switch next to the converter that allows me to shut it off without having to cut power to all the other receptacles in the trailer. Although I don't think that's necessary in your case, it is an option if you find out that the converter is somehow hardwired in such a way that turning breakers off won't kill the power to it.
30' Keystone Cougar 5'er, Triple Bunkhouse, SuperSlide.
Chevy 3500 1 Ton long box crew cab dually
6.5 Turbo Diesel, 4.11 Rears, LSD, Fresh rebuild spring 2012.
Dieselplace.com Staff Member

Our 2008 western adventure - to the coast and back!

Mark

Beachums
Explorer
Explorer
MrRchitty wrote:
Production date on your gensets?


I don't have them in front of me, but I can tell you that they were purchased about a month ago.
One is the Northern Tool (grey) and the other is a CPE (red). Aside from the oil fill provisions and color they look identicle. The grey is rated for 1700 continous watts, the red is rated for 1600.
2004 Ford Expedition 4X4 3.73 w/quick shift kit
Reese DC Straight Line/ Prodigy P2 Controller
2010 Coleman CT 250 GS

Beachums
Explorer
Explorer
PrivatePilot wrote:
You mentioned the parasitic load of your converter, but then you also mentioned that you had turned off all the circuit breakers except for the air-conditioner one. Are you suggesting that the converter is remaining on despite breakers being off?

If indeed your converter is still on that could certainly be the source of your problem.

You've also confirmed that your electric hot water tank is indeed isolated as well, correct?

It certainly sounds as if you're on the right track by switching off circuit breakers to try to isolate the air conditioner, but given as how some travel trailers are wired in such a bizarre fashion today it wouldn't surprise me if there's still a phantom load somewhere that you might be missing? With all of the breaker set in the same position that you've been doing this testing, the generators in Eco m ode, and the air conditioning switched fully off, when you plug the trailer into the generators is there any sort of RPM bump or sudden load (even for a split second) evident?




I may have this wrong, but it was my understanding that the converter/breaker/fuse was a single contained unit. If I was correct in this, it was my assumption that anytime the main breaker was on the converter unit is getting power even if the input breaker is opened. Perhaps, I am completely off base about this. But ultimately I am reasonably certain that everything else is isolated from the genset.

To answer you question about the power to the h20 heater, yes it is off. I am lucky enough to have manual switches for both wh functions.
2004 Ford Expedition 4X4 3.73 w/quick shift kit
Reese DC Straight Line/ Prodigy P2 Controller
2010 Coleman CT 250 GS

PrivatePilot
Explorer
Explorer
You mentioned the parasitic load of your converter, but then you also mentioned that you had turned off all the circuit breakers except for the air-conditioner one. Are you suggesting that the converter is remaining on despite breakers being off?

If indeed your converter is still on that could certainly be the source of your problem.

You've also confirmed that your electric hot water tank is indeed isolated as well, correct?

It certainly sounds as if you're on the right track by switching off circuit breakers to try to isolate the air conditioner, but given as how some travel trailers are wired in such a bizarre fashion today it wouldn't surprise me if there's still a phantom load somewhere that you might be missing? With all of the breaker set in the same position that you've been doing this testing, the generators in Eco m ode, and the air conditioning switched fully off, when you plug the trailer into the generators is there any sort of RPM bump or sudden load (even for a split second) evident?
30' Keystone Cougar 5'er, Triple Bunkhouse, SuperSlide.
Chevy 3500 1 Ton long box crew cab dually
6.5 Turbo Diesel, 4.11 Rears, LSD, Fresh rebuild spring 2012.
Dieselplace.com Staff Member

Our 2008 western adventure - to the coast and back!

Mark

bondebond
Explorer
Explorer
Beachums wrote:
MrWizard wrote:
Beachums
does your tt have a wall thermostat,
or are you using the controls on the roof top a/c

I ask because one tip/trick
is to turn the a/c on fan only for a few minutes , to allow air flow to reduce head pressure (cool compressor), the quickly turn the control to cool

another option (depends on ambient temperature) is to turn cool all the way off/down
turn on a/c
wait a few minutes , then turn cool to Max thus turning on compressor



I tried that too.... I am plugged into the gen set from the shore power cord. All but the main breaker and AC breaker are open (off). So other that the inherent parisitic loss of the converter circuitry, I just don't get where this thing is overloading.
The only other thing I can think of...... I have the electronic type overloads on the genset. If I remember and understand correctly from this thread, the older magnetic overloads were much more forgiving of inrush surge than the new ones.
I would pitch this one directly to Champion Customer Service directly, explaining what you have, what you've done, and what others have experienced (no problems with this kind of load and configuration) and see if they have a path to correct the situation. It might be a replacement of your control modules will resolve the issue and you can frustrate yourself to no end until something like that happens. I wouldn't hesitate any longer to give them "the ball's in your court". You've done everything needed to make it work, so it likely lies with the control modules, not knowing anything else of your configuration and setup.
This space left intentionally.

2006 Fleetwood Sequoia and mods...one of the tallest highwall pop-ups on the planet after flipping the axle.

MrRchitty
Explorer
Explorer
Production date on your gensets?
Randall J. Chittenden
CT
Fire/Medic
Former Auto Parts Sales 12 years

Beachums
Explorer
Explorer
MrWizard wrote:
Beachums
does your tt have a wall thermostat,
or are you using the controls on the roof top a/c

I ask because one tip/trick
is to turn the a/c on fan only for a few minutes , to allow air flow to reduce head pressure (cool compressor), the quickly turn the control to cool

another option (depends on ambient temperature) is to turn cool all the way off/down
turn on a/c
wait a few minutes , then turn cool to Max thus turning on compressor



I tried that too.... I am plugged into the gen set from the shore power cord. All but the main breaker and AC breaker are open (off). So other that the inherent parisitic loss of the converter circuitry, I just don't get where this thing is overloading.
The only other thing I can think of...... I have the electronic type overloads on the genset. If I remember and understand correctly from this thread, the older magnetic overloads were much more forgiving of inrush surge than the new ones.
2004 Ford Expedition 4X4 3.73 w/quick shift kit
Reese DC Straight Line/ Prodigy P2 Controller
2010 Coleman CT 250 GS

Beachums
Explorer
Explorer
PrivatePilot wrote:
Beachums wrote:
Okay, so I installed the spp6 across the compressor. It still goes into overload. I have it isolated. I have the gens out of Econ mode...... Trips it every time. I am pulling my hair and kicking the neighbors dog over the money wasted on this...... Any other ideas? Fwiw..... The ac unit is a dometic.


I would have ventured to say that something is wrong with your A/C and it'd drawing way more amps than it should be...but with a trailer that's only 2 years old this seems unlikely....yet not impossible.

I'd get a watts-up meter, plug it in between the generators and the trailer while plugged into shore power, and see what it shows for startup draw when you turn on the A/C.

When you installed the SPP6, did you leave the existing start cap in place and just piggyback the SPP6?



yeah, I just piggy-backed it.
Another thing, the existing run cap also feeds the fan motor.....is that normal?
2004 Ford Expedition 4X4 3.73 w/quick shift kit
Reese DC Straight Line/ Prodigy P2 Controller
2010 Coleman CT 250 GS

MrWizard
Moderator
Moderator
Beachums
does your tt have a wall thermostat,
or are you using the controls on the roof top a/c

I ask because one tip/trick
is to turn the a/c on fan only for a few minutes , to allow air flow to reduce head pressure (cool compressor), the quickly turn the control to cool

another option (depends on ambient temperature) is to turn cool all the way off/down
turn on a/c
wait a few minutes , then turn cool to Max thus turning on compressor
I can explain it to you.
But I Can Not understand it for you !

....

Connected using T-Mobile Home internet and Visible Phone service
1997 F53 Bounder 36s