Top Charge Question
Well it's been 33 days since I've seen hookups. The 245 watts of solar gets the Trimetric into the positive AH from full most days.
Specific gravity has dropped. A couple of cells to 1250, and a couple to 1260.
There are 4 x 6 volt batteries in two banks.
So at sunset tonight I'll switch to bank 2 and hit bank one with an hour of 15.3 volts from the Megawatt.
And then.... Bank 1 will have a higher voltage than bank 2. Is it ok to just switch back to 1+2? The voltages will equalize pretty quickly.
Or should I just stay on bank 2 for a week, switch to bank 2 and zap bank 1 with the megawatt? Then I can check weekly and zap the weaker bank as required.
The batteries are 232 AH so total nameplate rating is 464. Morning AH from full is averaging -30 so the batteries are living in their top 10%.
Joel