If you abuse any meter it will burn out. Your scare tactics are not valid. This is a 500A shunt! You need in excess of 500A for a fairly long time to burn this shunt.
In general, if a shunt does blow, it's the the fault of the shunt but the person who installed it. Shunts must be derated by 50%. If maximum current in a shunt application is limited to 50A, then use a 100A shunt. In the OP's case the shunt is rated 500A. It's overkill, but it will never blow. The battery in-line fuse will blow first.
As far as using shunts vs. hall effect, I believe shunts have more accuracy and can measure small currents.
BTW, that looks like an excellent meter. Go for it!
Sal
In general, if a shunt does blow, it's the the fault of the shunt but the person who installed it. Shunts must be derated by 50%. If maximum current in a shunt application is limited to 50A, then use a 100A shunt. In the OP's case the shunt is rated 500A. It's overkill, but it will never blow. The battery in-line fuse will blow first.
As far as using shunts vs. hall effect, I believe shunts have more accuracy and can measure small currents.
BTW, that looks like an excellent meter. Go for it!
Sal
pianotuna wrote:
I don't like the shunt because it IS possible for it to burn out.