Hi,
When I installed a new 5.7 GPM water pump, it's maximum draw exceeds my 7.5 amp relay. SO in 2003 I installed a 15 amp rated relay with a 24 VAC coil in the relay. It has worked fine for 10 years, don't think it could be a problem with the A/C unit.
Most 30 amp contactors are open type, where stray fingers around the contactor could get shocked if you touch the exposed shiny metal parts.
Many "Cube" relays are totally enclosed, and designed to fit into a socket, where changing the relay means unplug and plug in a new one. However most are only rated at max 10 or 12 amps. You could select a 10 amp 2 pole relay, then connect the compressor common wire to both poles, so that each will see only 1/2 the total amperage. 3 pole will also work well, with 1/3 of the amps per pole.
The indoor fan is only going to draw about 3 amps, so really easy to use a 1 pole cube relay. You can normally buy them in 12 VDC.
You will also need to decide if the fan will run on high speed or low speed, or install a switch to go between the two. You must never allow both speeds to be energized at the same time. You will also get a "Stray" voltage from the other speed. Such if you apply 120 volts to high speed, and the fan is running, then you might have 90 volts on the low speed wire. When you have 120 volts applied to the low speed, then you might have between 130 and 145 volts at the black high speed wire. Should you put 120 volts to both windings at once, your fan will not last long, and will require replacement soon.
Most thermostats only have one fan speed selection. Some RV thermostats have a high fan and low fan selection, so you can run high speed on warm days or while driving, and low speed at night so it is quiet.
Good luck,
Fred.