Hi KD4UPL.
Here is some real life testing (pay attention to the column for gallons per KWH):
15 kW portable Generac. Regular gas, fixed 3600 rpm.
No load , 0.8 gal/hr
25% load, 3.75 kW, 1.0 gal/hour, 3.8 kWH's/gal.
50% load, 7.5 kW, 1.3 gal/hour, 5.9 kWH's/gal.
75% load, 11.25 kW, 1.6 gal/hour, 7.0 kWH's/gal.
100% load, 15 kW, 1.8 gal/hour, 8.3 kWH's/gal.
Yamaha EF3000is, regular gas, variable rpm, ECO control on.
No load, 0.12 gal/hour.
25% load, 0.7 kW, 0.17 gal/hour, 4.1 kWH's/gal.
50% load, 1.4 kW, 0.32 gal/hour, 4.4 kWH's/gal.
75% load, 2.1 kW, 0.47 gal/hour, 4.5 kWH's/gal.
100% load, 2.8 kW, 0.60 gal/hour, 4.6 kWH's/gal.
Note that at 75% and 100% load a traditional generator is nearly twice as efficient as an inverter generator, so if you plan on running an air conditioner a (small) traditional generator may be a better choice.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.