Forum Discussion

jjrbus's avatar
jjrbus
Explorer
Feb 09, 2015

Supco SPP6E HELP!!

My Honda EU200i barely starts my AC unit (spec's to follow) I did some reading and decided that the SPP6E might help?? I ordered one and did some further reading and became convinced that the SPP4E would be the right one?

I have been waiting for delivery and a ERPP6 showed up in the mail! I am 100% sure of what I ordered, http://www.amazon.com/dp/B002JP3MEK/ref=pe_385040_128020140_TE_3p_dp_1

My first inclination is to return this, but will ask if it might be the better one for the job at hand?
http://catalogs.service.com/mfgs_pdfs/4277/1249074886_0001_0029.htm

It says replacement for SPP6, HS650, WSX-6, 115-277V, 4000 to 120,000 BTU with solid state design, 1/2 thru 10 HP.

My unit is a 11K BTU Brisk air model 57912.602 I don't see how to add a scan here?

The schematic shows a Fan, Herm as one unit, seperate PTCR and round start cap. I have not had the cover off the unit so do not know what is really there!


Any other info needed? JIm SW FL

Moderator edit to fix links.

4 Replies

  • Thanks for the responses!

    As I read through megabytes of info and misinformation I cannot help but wonder? If I should start by replacing my original PTCR and start capacitor?

    I have no way to test these, the AC starts and runs when plugged into house, but struggles to start on the Honda EU2000i. Could that be a weak start capacitor?

    JIm SW FL
  • The Supco SPP6E is rated at 208 to 277 volts, not the 120 volts that you would need.

    The SPP4E is rated at 100 - 130 volts, just right!

    http://www.supco.com/web/supco_live/product.php?department=1&category=1&subcategory=1 You can look up the specs on each here.

    You might be looking at a PTC booster. They do not have the instant recycling ability, in other words they use a resistor that gets really hot, then the resistance increases, taking the capacitor out of the wiring circuit. Then it MUST wait about 4 minutes to cool enough that the capacitor can work effectively again. If still hot, it will not do any good. So if the compressor does not start in 5 seconds, it will still be to hot when the compressor overload tries to start it again, but the capacitor will not be able to assist.

    The SPP4E will recycle instantly. So if the compressor does not start, the compressor internal overload trips, and resets in about 45 seconds, then the compressor needs 'extra' help to restart, the SPP4E will be ready to start the compressor (even after 4 seconds of wait time).

    The SPP6E rated at 200 - 250 volts will also 'work' but will wait until it has over 190 volts across the terminals to 'drop out' the capacitor. While the E-series does have a electronic drop out after a few seconds. However it is much better to drop out at 120 volts (once the compressor is up to speed, and less than 2 seconds most of the time) to lessen stress on the compressor start winding.

    Good luck

    Fred.
  • I put the same unit in my 13.5 BTU AC unit. I still need (2) 2000 yamaha to start the AC. The capacitor just made it easier on the generators.