spud1957 wrote:Coach-man wrote:spud1957 wrote:RedRam wrote:
I'm looking at those power cords and it says 30' 16/3-8/1 Cord 125-240V.I take it as 3 strands of 16 guage and 1 strand of 8 guage as that makes up the four strands.That seems awful light to me if i'm reading it right.
16g cable is not rated at 50amps. Perhaps you meant 6/3?
10g = 30a, 8g = 40a and 6g = 50a.
16g? That is close to telephone wire, certaintly not power cord!
I know it's not on topic but phone wire is 24g.
I never said it was, I said close, some old phone cable used 18 gauge wire! And IMHO it is not really off topic, if anyone were to use 16 gauge wire for a 50 amp cord, it would be a real problem.