BB_TX wrote:
theoldwizard1 wrote:
Just make sure the A/C units are on different "legs" of the 240V feed.
..........
Over simplifying. Balancing is a good idea. But before wiring in a 2nd A/C you need to look at how distribution is already done. If the existing A/C is on hot leg 1; and the water heater, microwave, converter, and that outlet used to operate the DW’s 1500 watt hair dryer are on hot leg 2, then hot leg 2 already far exceeds hot leg 1. Adding the 2nd A/C to hot leg 2 would compound the problem. In that case putting the 2nd A/C on hot leg 1 would make more sense. Or better, move some things from hot leg 2 to hot leg 1 before adding the 2nd A/C to hot leg 2.
Two A/Cs are 30 running amps or less. That is only 60% of the full 50 amps available for one leg if no other high current device is also connected to that hot leg.
Need to look at the big picture.
Great advice. Absolutely no reason why 2 A/Cs can't be on the same leg. Take this advice and look at the big picture.