GFCI

We have just brought home (new to us) a 2015 Cruiser Aire fifth wheel. Plugged it into our outside 20A outlet and it trips the GFCI. I have isolated the problem to the 15A microwave circuit. I have unplugged the microwave and used a circuit tester to verify that it wired correctly.
On this circuit there is only the circuit breaker, wire, and outlet. Should I assume the circuit breaker is the cause?
  • It is most likely in the wiring between the microwave breaker and outlet; or, at the outlet itself. It could be the black (hot) wire touching the ground. It could also (more likely) be the white (neutral) wire touching ground. Either will cause the GFCI to trip.
  • There is a good chance that the White (neutral) and Ground are touching. If the plug for microwave is easy to get to pull the plug out and look at wiring. You can try taking the plug off and separating the wires. You can also look at the trailer breaker box and make sure the White and ground are not together.

    Let us know what you find.
  • If everything is ok with the microwave unplugged then the problem is an internal one with the microwave. Trips as soon as you plug it in, or, as soon as you turn the micro on?
    Not unusual. Common with blow dryers plugged into bathroom GFI. One blow dryer trips another won't.

    Plug something else in the micro outlet and see what happens or if you have another microwave plug that in.
  • I checked for a junction box and / or wires under the slide. Saw no issues. Pulled the cover off the breaker box in the RV and found the wire for that circuit were tight and connected correctly. Tomorrow, I will remove the wires from the outlet and see if that fixes the issue.
  • Masscamper wrote:
    I checked for a junction box and / or wires under the slide. Saw no issues. Pulled the cover off the breaker box in the RV and found the wire for that circuit were tight and connected correctly. Tomorrow, I will remove the wires from the outlet and see if that fixes the issue.


    Keep at it your doing all you can. Keep us posted.
  • After a break from all the rain, the GFCI has stopped tripping at home. We have been out for a couple more weekends away and no problems there either. I'm still keeping my eyes open for the cause.
  • Also, I have found that if you plug a GFCI device into a GFCI outlet it will trip.
  • So one of the main things a GFCI does, is measure that all current going out the hot is returned on the common neutral. So somewhere in the MW circuit it is leaking current on the hot lead. As you stated that the minute you turn on that breaker, the GFCI trips even without the microwave plugged. Moisture in a slide junction box or cable comes to mind.