The Honda EU2000i (and the Yamaha EF2000is, a pair of which I use in parallel) have floating (ungrounded) neutrals. The Progressive Industries power protection system in our 5th wheel will error out with an E9 error message if the 5th wheel is plugged straight into the paralleled Yamahas' 30 amp outlet when a floating neutral is present.
Without getting into a discussion of ground loops and code requirements that neutral be bonded to ground ONLY at the main power distribution panel, the solution to this issue is to use a Neutral-to-Ground bonding plug in one of the 120VAC 15/20 amp outlets of one of the generators. These plugs (which you can easily make yourself) jumper the neutral terminal to the ground terminal at the generator, thus making the generators' 30 amp receptacle look like a 30 amp shore power receptacle to the power protection system.
With neutral and ground bonded, the meter readings on the 30 amp receptacle should look like this:
The Neutral-to-Ground bonding plug looks like this (cover removed):
Rusty