SoundGuy wrote:
RustyJC wrote:
Insofar as the advisability of bonding Neutral to Ground, I would refer you to the following ARTICLE.
As with anything just because you read it on the internet doesn't make it so. ;) Progressive Industries is a big supporter of the author of The No Shock Zone yet specifically warns against bonding. Anyone who really wants to try to understand the issues involved should take the time to forge through these 41 pages of discussion, wherein not even the "experts" could agree. I have, and personally I'd suggest anyone considering bonding not do so until they have a much clearer understanding of the issues involved.
Last year I had this same or similar issue. I contacted Progressive with the following:
I have installed an EMS-HW50C in my 5th wheel.
I also have a Yamaha 3000ISEB generator that I rarely use with the 5th.
However, I have noticed I have to flip the switch to turn off the EMS on the remote monitor of the EMS or I do not get any power into the trailer.
Is there a way to get around this and use my Yamaha and still have the protection of the EMS?
Or because I am solely connected to the Yamaha, do I not need to worry about protection with the EMS?
PI response was such:
Regarding the use of an aftermarket generator, yours is a common problem. It
is caused by the fact that there is no connection between the generator and chassis ground, this is
seen as an open ground by our device. This message has a pdf file attached that will show you how
to solve this problem. Once you do this there will be no need to switch the HW50 off and you will
have full protection again. Thank you for using our product. Regards, Donald Customer ServiceThe PDF file noted the following:
Special Generator Adapter Instructions
Items Needed:
1 X 15A Male replacement plug (Picture A)
1 X Short 16-12awg wire (1-3”)
Instructions:
1. Open male replacement plug.
2. Identify wire locations (ground, neutral, hot).
3. Connect 16-12awg short wire between neutral (white) and ground (green) inside replacement plug (Picture C).
4. Close plug.
5. Insert new plug/adapter into a free outlet on generator.
Warning: Use only when running on a portable generator. Never use on standard shore power/landline!
An FYI