kelly4hand wrote:
This is a private site, with one pole and 4 - 30 amp plugs. We will be the only camper plugged in. Owner states" just need to put bigger wiring to make it 50 amp"....but he is honesty quite old...lol so going to have an electrician look at it...
Our 50 amp RV's use 2 legs of 120v, or actually its 240v being supplied but not being used as a 240 service.
Our gennys also use the same type service, thats why we have 2 breakers on our RV genny service. Each beaker protects one 120v leg of the 240 volt service coming from the genny.
Each leg of a 50amp rv service can supply up 25-30 amps for a combined amp draw of 50a, 120v.
This can be measured on the common neutral leg with an amp probe.
Just be sure your cheater cord is rated for 50 amps thru its common neutral leg... Since the neutral leg is not protected by a circuit beaker. Neutral leg wire in the cheater cord should be at least #8 wire, #6 is better.
So bottom line for you, get a multi-meter and find the 2 outlets that have separate legs of 120v.Your meter test leads will need to be in 2 different outlets, measuring the hot wires between both outlets.
You need to get a 240v reading from both hot legs read together. If you are only getting 120v then both outlets are on the same leg and will not give you the 50 amps you want. Keep trying different outlet combinations till your meter reads 240v, and then use these 2 outlets with the cheater cord. This will give you 2 separate legs of 120v, combined for 50 amp 120v capability.
jmo