pianotuna wrote:
Hi WesternRVparkowner,
That's a nice factoid on the 7 fifty amp circuits on a 200 amp breaker. Thanks for sharing it.
Of course even large RV's with twin 15000 btu air conditioners going "flat out" are only drawing about 3000 watts (~25 amps). So 25 X 7 is still only about 175 amps of that 200.
Does anyone complain of voltage drop?
Never have voltage problems. I spent the money and have rock solid electrical systems and I service the connections regularly. You haven't been to many RV parks and looked at the big rigs lately, have you? The trend now is all electric coaches, three and 4 air conditioners and all the trimmings. But that is the reasoning behind the NEC. All four air conditioners are usually not running at the same time, and they surely aren't all starting at the same time. Then all 7 rigs aren't running their vaccum cleaners and microwave ovens and electric cooktops, while blow drying their hair at the same time as everyone else. The loads will spike at one rig and valley at another. In the end, neither of the 200 amp legs will ever exceed 200 amps at any given moment, even though the pedestals give a potential of 350 amps per leg. Hence why the NEC calculates loads instead of just adding up potential.