Forum Discussion
enblethen
Jul 07, 2017Nomad
I would go into the 120 volt distribution panel and look for heat damaged insulation and discoloration.
Turn off power, remove metal dead front to gain access.
Pick up a tube of electrical grease from your local hardware store.
Disconnect each conductor, one at a time, clean coat with the electrical grease and re-connect.
Do this to each of the neutrals(white wires) and each of the phase connections on breakers and buss work.
A poor connection will increase resistance which increases amperage on circuit.
Turn off power, remove metal dead front to gain access.
Pick up a tube of electrical grease from your local hardware store.
Disconnect each conductor, one at a time, clean coat with the electrical grease and re-connect.
Do this to each of the neutrals(white wires) and each of the phase connections on breakers and buss work.
A poor connection will increase resistance which increases amperage on circuit.