Anyone running 3 15M AC's on 50 amp? Follow up added

We have been told we can but not advised. With almost everything else off except residential fridge it is still too close to limits of available juice. Wondering if others do actually run 3 units and how it has worked out. Thanks

We did use all three coolers for most of yesterday afternoon and it cooled nicely. Thanks everyone for the info.
  • Would not hurt to measure AC draw.
    My 15k Carrier draw 8.2 amp while running, so theoretically I could run 3 of them on 30 amp service, but the motors have huge spike while restarting and that is why they require bigger power line.
    Common sense if you want to use 3 of them is to set thermostats on 2 to low and let the 3rd one cycle when it gets too cold.
    That will avoid the potential situation when 2 might want to restart in the same time.
  • rgatijnet1 wrote:
    ...50 amp service is actually 100 amps total...


    Yes...two legs with 50 amps each. It will run three ACs easily.
  • Thanks everyone. We have been in a CG with no trees and 95+ temps and humidity for several days. Two units does well until about 3:00 or so and then the cabin looses a little ground. We'll go ahead and turn on the third unit today.
  • Your signature indicates you are operating a Newmar Dutch Star... Newmar coaches will run 3 ACs and oodles of other "stuff" without breaking a sweat!! You were told WRONG my friend!! Not to speak heresy, but I would suggest you also join the IRV2 Forums and link to the Newmar owners section! The information available there is unbelievable!!
  • No problem if proper 50 amp RV service (two 50 amp hots) AND properly wired coach (one each A/C on each hot leg).
  • One of the units needs to be on the other leg. There are 6000 watts available on each leg. In theory four units could be run, two on each leg.
  • True 50 amp service is actually 100 amps total. Three AC units should be able to run, along with other appliances IF all three AC units are NOT wired to one leg of the 50 amp input. If all three are wired to one leg on the incoming service, than 50 amp is the limit on the AC units, but that should not affect the other appliances on the other 50 amp leg of service.
    Of course if all of the AC units are wired on one leg and that leg trips on the park pedestal, it will shut off both legs since the breaker is tied together.