GFCI is not a surge device. It won't trip from an overload, only from a ground fault.
15 amps should not be run at more than 12 amps continuously. Translating that to watts means you can use any combination of devices that total up to 1440 watts.
I run oil filled type heaters that have switches so I can reduce the load. It is best to measure each device with a kill-a-watt meter.
I carry #12 cords for running from residential outlets.
15 amps should not be run at more than 12 amps continuously. Translating that to watts means you can use any combination of devices that total up to 1440 watts.
I run oil filled type heaters that have switches so I can reduce the load. It is best to measure each device with a kill-a-watt meter.
I carry #12 cords for running from residential outlets.