Old-Biscuit wrote:
Sounds like furnace is starting correctly and lighting main flame but then looses main flame......
Circuit board HAS to receive a 'signal' generated by main flame proving that it is lit. Without that signal.....circuit broad secures dc power to gas valve and lets is close.
Things that cause issue:
Exhaust blocked.......mud dabbers/nests outside vent
Spark electrode not positioned directly over main burner slots where it is engulfed in main flame
Spark electrode ceramic cracked......signal shorts to ground
Dirty/loose/poor connection of spark electrode wire at circuit board
Dirty/loose/poor connection on circuit board multi-wire connector
I'm with Biscuit on this and think that because of the age of the coach, if screens were not installed over the vents daubers have gotten in and built mud nest to restrict air flow. I faught this problem last year in my TT on my deer lease. Finally put screens on. Resolves the problem, but only after furnace is cleaned.