There is a problem with the hypothesis. The GFCI compares the current flowing thru the hot connection to the current flowing thru the neutral connection. A difference of 5-6 milliamps will cause a trip of the GFCI. That current flow should be exactly the same in both. If there were 5 amps flowing thru the hot wire (and therefore 5 amps flowing thru neutral) and it induced 10 milliamperes current thru the ground wire, that does not mean there would be any change in the flow thru hot and/or neutral. Those current flows would still remain identical unless there were a leakage somewhere. And an induced flow in a ground wire is not leakage and would not cause s trip. The GFCI does not do a compare to the ground wire.