i want to add something here , food for thought
he already has a 6500 LP generator
thats what ? 28 amps per leg, 56 amps max possible full load, on the neutral
in a strickly 120, 120 parallel in phase windings
8000w another 5amps per leg, a max possible 10amps increase on the neutral
do you really thing, the wiring is so weak, so undersized, that it is NOT going to handle that increase ?
I don't
he already has a 6500 LP generator
thats what ? 28 amps per leg, 56 amps max possible full load, on the neutral
in a strickly 120, 120 parallel in phase windings
8000w another 5amps per leg, a max possible 10amps increase on the neutral
do you really thing, the wiring is so weak, so undersized, that it is NOT going to handle that increase ?
I don't