THE-RV-MAN wrote:
I started the generator and turned on the roof air and it did not work. The microwave time came on but when I tried to turn it on the time would count down but would not spin. I checked all the fuses and the converter box had a fuse fried. I changed it and still did not work. All wires and fuses look good. I plugged into shore power and everything worked perfect. Generator starting up no problem. I'm confused. Can someone help me on this. Can someone help.
You must first establish if the generator is putting out any voltage, so try something in the 120vac outlets to be sure. If not then it's possible the the gen set itself isn't putting out for whatever reason. If you have a plug-in receptacle for that, then it should be easy to check. If not and you have a transfer switch then you should be able to check there. Either that or remove what panels are necessary on the genset to check for voltage at it's circuit breakers. Some of your appliances require 12vdc control voltage to operate, so this further checking is necessary for finding the root of the problem.