want-a-be wrote:
We have a Magnum Energy System. We have it set for the generator to start when the voltage gets low, sometimes it starts when we are not there and it is still running when we come home. Is there a way to tell how long it has been running!
Thanks for all comments!
Your ME-ARC50 remote will have that information. Consult page 58 of the owner's manual. On the remote, go into the METER menu, and then AGS... excerpt from the manual:
METER: 04C Gen Run Time Menu
This read-only menu displays the length of time the generator has been running since it was
autostarted. This helps determine how long the generator has been running since it was autostarted—in
case you were not present when it started. This menu is enabled when CTRL: 03 Gen
Control is set to AUTO, but does not display run time when the generator has been manually
started. This meter is not designed to replace an hour meter that shows the total hours the generator
has run—refer to the METER: 04G Hour Meter menu.