From my service manual for HDKAJ, HDKAK, HDKAT:
GOVERNOR ACTUATOR FAULT—CODE NO. 19
(Controller sensed open or short circuit)
1. Remove the front housing panel (p. 6-4) and reconnect the engine wiring harness connectors E1-1 and E1-2 to the governor actuator if they are loose. Polarity does not matter (p. 19-1, 13-1).
2. Measure actuator coil resistance with a digital ohmmeter. Replace the actuator stator assembly if coil resistance is not 1.7 to 2.8 ohms.
3. Disconnect engine harness connector P1 from the controller assembly (p. 19-1, 19-4). Check for electrical continuity between pin P1-1 and quick connector E1-1 and between E1-2 and ground. Replace the engine harness if either leg lacks electrical continuity. Also check for missing, bent or corroded terminals and connector pins and repair or reconnect as necessary.
GOVERNOR ACTUATOR FAULT—CODE NO. 19
(Controller sensed open or short circuit)
1. Remove the front housing panel (p. 6-4) and reconnect the engine wiring harness connectors E1-1 and E1-2 to the governor actuator if they are loose. Polarity does not matter (p. 19-1, 13-1).
2. Measure actuator coil resistance with a digital ohmmeter. Replace the actuator stator assembly if coil resistance is not 1.7 to 2.8 ohms.
3. Disconnect engine harness connector P1 from the controller assembly (p. 19-1, 19-4). Check for electrical continuity between pin P1-1 and quick connector E1-1 and between E1-2 and ground. Replace the engine harness if either leg lacks electrical continuity. Also check for missing, bent or corroded terminals and connector pins and repair or reconnect as necessary.